Schneider ATS48 Soft Starter Remote Start/Stop via Modbus

Schneider ATS48 Soft Starter Remote Start/Stop via Modbus

Schneider ATS48 Soft Starter Remote Start/Stop via Modbus

(OP)
Hi,

I have ATS48 Softstarter circuit as shown in the attached PDF. In "Manual" mode, I can start the motor from MCC Start button and the "Run" Logic input in the Starter received signal so it closed R1 and subsequently R2 dry contacts inside the Starter so K1 and K3 contactors energized and the motor is working fine.

But in Remote mode, the control is via modbus serial communication from PLC. When I start from SCADA, nothing is happening.

Somebody told that I need 3phase supply to Starter. Then only the "Run" logic input in starter will receive input from SCADA via modbus. Do we really need 3 phase to present in the starter before start from SCADA using modbus serial communication? I don't think it is required. We already have control supply to the starter. I suspect it is a communication cable or PLC program issue. Anybody who has experience on ATS48 please advise on this matter.

Replies continue below

Recommended for you

RE: Schneider ATS48 Soft Starter Remote Start/Stop via Modbus

Hello Histor,

Can you confirm that you have successfully established a modbus connection with the ATS48?

Do you have the ATS48 Modbus Protocol manual ?
https://www.se.com/us/en/download/document/VVDED30...

Do you have created a state machine to go throw the DRIVECOM state chart like on Page 21?


RE: Schneider ATS48 Soft Starter Remote Start/Stop via Modbus

To setup remote control for ATS48 need a special procedure.
Check this link: https://www.se.com/ww/en/faqs/FA317313/
Need to configure also all parameters from COP (communication menu); check manual of ATS48.

RE: Schneider ATS48 Soft Starter Remote Start/Stop via Modbus

(OP)
Can I start from SCADA if the status on Starter shows "nLP"?

RE: Schneider ATS48 Soft Starter Remote Start/Stop via Modbus

Are you receiving/reading ETA (W458) = 16#xx21?

RE: Schneider ATS48 Soft Starter Remote Start/Stop via Modbus

To answer the first question though, you do NOT need the 3 phase power on the soft starter line terminals first. If that were the case, it wouldn’t work in Local mode either, because K1 would not close.

So yes, this is a ModBus protocol issue.


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden

RE: Schneider ATS48 Soft Starter Remote Start/Stop via Modbus

(OP)
Hi Jraef,
In local mode it works fine as I give Run Signal by energizing K11 relay. Once I give Run command the internal starter dry contact (R1A-R1C) closes and it will energize K1.

RE: Schneider ATS48 Soft Starter Remote Start/Stop via Modbus

Hello Histor,

Still didn't answer my questions. Can you confirm that you have successfully established a modbus connection with the ATS48?
Are you receiving 16#xx21 value when reading ETA (W458) register when Starter shows "nLP"?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close