Schneider ATS48 Soft Starter Remote Start/Stop via Modbus
Schneider ATS48 Soft Starter Remote Start/Stop via Modbus
(OP)
Hi,
I have ATS48 Softstarter circuit as shown in the attached PDF. In "Manual" mode, I can start the motor from MCC Start button and the "Run" Logic input in the Starter received signal so it closed R1 and subsequently R2 dry contacts inside the Starter so K1 and K3 contactors energized and the motor is working fine.
But in Remote mode, the control is via modbus serial communication from PLC. When I start from SCADA, nothing is happening.
Somebody told that I need 3phase supply to Starter. Then only the "Run" logic input in starter will receive input from SCADA via modbus. Do we really need 3 phase to present in the starter before start from SCADA using modbus serial communication? I don't think it is required. We already have control supply to the starter. I suspect it is a communication cable or PLC program issue. Anybody who has experience on ATS48 please advise on this matter.
I have ATS48 Softstarter circuit as shown in the attached PDF. In "Manual" mode, I can start the motor from MCC Start button and the "Run" Logic input in the Starter received signal so it closed R1 and subsequently R2 dry contacts inside the Starter so K1 and K3 contactors energized and the motor is working fine.
But in Remote mode, the control is via modbus serial communication from PLC. When I start from SCADA, nothing is happening.
Somebody told that I need 3phase supply to Starter. Then only the "Run" logic input in starter will receive input from SCADA via modbus. Do we really need 3 phase to present in the starter before start from SCADA using modbus serial communication? I don't think it is required. We already have control supply to the starter. I suspect it is a communication cable or PLC program issue. Anybody who has experience on ATS48 please advise on this matter.
RE: Schneider ATS48 Soft Starter Remote Start/Stop via Modbus
Can you confirm that you have successfully established a modbus connection with the ATS48?
Do you have the ATS48 Modbus Protocol manual ?
https://www.se.com/us/en/download/document/VVDED30...
Do you have created a state machine to go throw the DRIVECOM state chart like on Page 21?
RE: Schneider ATS48 Soft Starter Remote Start/Stop via Modbus
Check this link: https://www.se.com/ww/en/faqs/FA317313/
Need to configure also all parameters from COP (communication menu); check manual of ATS48.
RE: Schneider ATS48 Soft Starter Remote Start/Stop via Modbus
RE: Schneider ATS48 Soft Starter Remote Start/Stop via Modbus
RE: Schneider ATS48 Soft Starter Remote Start/Stop via Modbus
So yes, this is a ModBus protocol issue.
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
RE: Schneider ATS48 Soft Starter Remote Start/Stop via Modbus
In local mode it works fine as I give Run Signal by energizing K11 relay. Once I give Run command the internal starter dry contact (R1A-R1C) closes and it will energize K1.
RE: Schneider ATS48 Soft Starter Remote Start/Stop via Modbus
Still didn't answer my questions. Can you confirm that you have successfully established a modbus connection with the ATS48?
Are you receiving 16#xx21 value when reading ETA (W458) register when Starter shows "nLP"?