Prying Action - Floorbeam to Girder Double Angle Connection
Prying Action - Floorbeam to Girder Double Angle Connection
(OP)
I am designing a double angle connection between a floorbeam and a girder web on a bridge. The floorbeam is coped, has a 6.5" eccentricity to 15 bolts 3/4" A992 bolts spaced at 3", and has a load of 308 kips at the girder. I am having some trouble coming up with the required strength, T. Can I extrapolate T from the moment created by the eccentric point load? Would I even need to account for the prying action in this case?
RE: Prying Action - Floorbeam to Girder Double Angle Connection
Also note bolts are not A992, they are A325/F1554 or A490 (not sure off the top of my head the F designation). Make sure you are using the appropriate allowable stress for your bolts based on the selected grade.
RE: Prying Action - Floorbeam to Girder Double Angle Connection
Remember to check the moment at the end of the cope.
RE: Prying Action - Floorbeam to Girder Double Angle Connection
RE: Prying Action - Floorbeam to Girder Double Angle Connection
That's where Tbolt = (6Me/(b*d^2))*At*keff comes from. (Refer to "Steel Structures - Design and Behavior" by Salmon and Johnson for a full explanation.)
Me = V*ex + P*ey is just the moment due to the eccentricity of the shear and axial loads (see graphic below).
Finally, T = Tbolt + P/(n*b) is actually T = Tbolt + P/(nb), where nb is one variable for the number of bolts, so they are just combining Tbolt (which was determined above) with the tension in the member divided evenly amongst all of the bolts.