More On Wye Wye Connected Transformers

More On Wye Wye Connected Transformers

More On Wye Wye Connected Transformers

(OP)
thread248-481670: Wye-Wye Transformer and grounding

In the United States, in underground mining applications it is legally required that the source secondary transformer have a neutral point, and the neutral must be grounded through a resistor. The resistor value is chosen to limit the maximum phase to ground fault current to 15 amps or less. For a 3 phase 600 volt system, the resistor value will be 23 ohms or more. In all cases, the source transformer’s primary is delta connected. All loads on the transformer secondary are connected phase to phase. Ground fault detection relays are utilized for instantaneous tripping of the branch circuits if a phase to ground fault condition occurs.

After reading the preceding discussion, it appears that a primary wye connection whose neutral point is solidly grounded will permit secondary zero sequence current to flow. Furthermore, it appears that the magnitude of secondary zero sequence current will in essence only be impeded by the resistor.
Agree or disagree?

Thank You, Jim

RE: More On Wye Wye Connected Transformers

Quote (OP)

All loads on the transformer secondary are connected phase to phase.
So the only time current can flow into the neutral point via the NGR is during a fault. Therefore there can't be any third harmonic passing through the NGR, except when the system experiences a ground fault.

RE: More On Wye Wye Connected Transformers

Mr JWLunden (Electrical)(OP)30 Mar 23 23:23
".... #1. In all cases, the source transformer’s primary is delta connected. All loads on the transformer secondary are connected phase to phase. Ground fault detection relays are utilized for instantaneous tripping of the branch circuits if a phase to ground fault condition occurs.
#2. After reading the preceding discussion, it appears that a primary wye connection whose neutral point is solidly grounded will permit secondary zero sequence current to flow. Furthermore, it appears that the magnitude of secondary zero sequence current will in essence only be impeded by the resistor..."

1. If the trafo secondary in Y and the Neutral is grounded through NGR, why "Ground fault detection relays are utilized for instantaneous tripping of the branch circuits if a phase to ground fault condition occurs" ? A small time delay say < 1s would be desirable.
2. If the trafo primary is in D, the secondary is Y, with Neutral grounded directly or through NGR; any ground fault on the secondary will be within the secondary circuit only.
2.1. If the trafo primary is in Y with Neutral grounded, the secondary is Y with Neutral grounded directly or through NGR; any ground fault on the secondary will be limited in the secondary circuit only.
Che Kuan Yau (Singapore)

RE: More On Wye Wye Connected Transformers

Ignoring the resistor for a moment, for a grounded wye - grounded wye transformer there will generally be LESS line-to-ground fault current on the secondary side compared to a delta-wye transformer, due to inclusion of the primary side zero sequence impedance in the circuit. In a delta-wye transformer, the wye-side zero sequence current is sourced by the transformer itself since Io can flow in the delta limited mainly by the transformer impedance. The fault current is not much influenced by how the loads are connected. Adding a neutral grounding resistor will limit the fault current in similar manner for either a grounded wye or a delta primary.

RE: More On Wye Wye Connected Transformers

Well, with Y-Y connected transformer the transformer impedance and primary zero sequence impedance will be in "series" with the grounding resistor. But, in practice the grounding resistor is such a high impedance compared to the others that it is the only impedance that needs to be considered when calculating the secondary ground fault current.

RE: More On Wye Wye Connected Transformers

(OP)
I want to thank everyone for their helpful posts. In response to che12345, in mining applications the ground fault trip for each branch circuit must be instantaneous. A ground fault condition is considered an emergency, and the power must be removed to prevent shock and/or electrocution. The loads are fed by portable trailing cables that are very prone to damage. Men operating the machines are in immediate danger during a ground fault.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now