Spreadbored Pile Spacing
Spreadbored Pile Spacing
(OP)
I have a current project where the equipment loading requires a small slab. The slab is small enough that the pile spacing is less than the 3x spacing stipulated in the geotech report. The soil is cohesive, a sandy silt.
Is there a method of safely approximating the proximity of the piles to the end bearing capacity? The bells do not overlap. I suspect the spacing is related to the 'pressure bulbs' overlapping at the bottom of the spreadboreds. Is there a means of accommodating this? It doesn't seem possible to get info from the geotech that did the original report. The factored equipment weight (as DL) is of the magnitude of about 100K in an area, of the slab, of approx 6' x 8'. The centres of the 24" dia spreadbored piles is 1' from the edge of the slab.
-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates
-Dik
Is there a method of safely approximating the proximity of the piles to the end bearing capacity? The bells do not overlap. I suspect the spacing is related to the 'pressure bulbs' overlapping at the bottom of the spreadboreds. Is there a means of accommodating this? It doesn't seem possible to get info from the geotech that did the original report. The factored equipment weight (as DL) is of the magnitude of about 100K in an area, of the slab, of approx 6' x 8'. The centres of the 24" dia spreadbored piles is 1' from the edge of the slab.
-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates
-Dik
RE: Spreadbored Pile Spacing
This layout is even better, recommended 3x spacing is available on the 8' side. This results in two groups, two piles in each group... the two piles in each group tend to interfere with each other for only a small portion of their circumference.
Also, since the groups are "small" and the piles are bored (not driven displacement piling) there will be no problem with pile heave.
I would not be concerned, 100k should not be a problem for four properly designed piling with this spacing.
Note: I was not familiar with the the term "spreadbored", but a little time on Google makes me believe this what I would call a "bell caisson":
RE: Spreadbored Pile Spacing
First time playing draftsman for a couple years...
Thanks, SRE.
-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates
-Dik
RE: Spreadbored Pile Spacing
Well, then provide it... forget the belled caissons and use a true pile group with 3x spacing to mobilize the entire 6' x 8' soil block down to bearing elevation. See if the Geotech will go with a dozen 8" drilled shafts at 24" on center:
RE: Spreadbored Pile Spacing
Installing those 12 piles would be a lot more costly than widening the slab by 2', I suspect.
-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates
-Dik
RE: Spreadbored Pile Spacing
If a slab 8 ft. x 8 ft. will solve the problem... why didn't you do that to start with... cheapest concrete ever poured. I assumed there was no space for a larger slab...
or
Drive a dozen, or so, HP8x36 and be done with it, a pile group is better anyway (spread the load more uniformly and redundancy).
RE: Spreadbored Pile Spacing
-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates
-Dik
RE: Spreadbored Pile Spacing
www.PeirceEngineering.com
RE: Spreadbored Pile Spacing
-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates
-Dik