Excess camber growth
Excess camber growth
(OP)
We have a small bridge under construction, 60' long x 60' wide. The superstructure is prestressed adjacent box beams. 10 box beams being erected in two stages. Stage 1 is finished. The fabricator is shipping the beams tomorrow morning; they're supposed to be erected tomorrow night. A little bit of a problem. One beam has a camber of 5 1/8"; the theoretical camber due to prestress and growth is 2 1/2". I think we have a solution to get the post-tensioning ducts to line up, but what's bothering me is the excess camber.
I don't have a lot of experience with prestress. I can see a measured camber was 25% higher than theoretical as the high end but 100% is odd, to say the least. Maybe Eci was very low and the QA inspector missed it? Any thoughts?
I don't have a lot of experience with prestress. I can see a measured camber was 25% higher than theoretical as the high end but 100% is odd, to say the least. Maybe Eci was very low and the QA inspector missed it? Any thoughts?
RE: Excess camber growth
I don't know how your contract is written, but that would be way outside the specified camber tolerance for us, and therefore would be cause for rejection of the girders. That's probably what would happen if they showed up at the site like that.
Excess camber would likely produce excess tension in the concrete of the top flange, which will severely shorten the superstructure service life where salt is used.
RE: Excess camber growth
No draped strands. The camber tolerance is +/- 3/4" along the box & 3/4" between adjacent units. However, the owner's plant inspector is only flagging the tolerance between adjacent boxes.
RE: Excess camber growth
RE: Excess camber growth
RE: Excess camber growth
RE: Excess camber growth
RE: Excess camber growth
RE: Excess camber growth
RE: Excess camber growth
RE: Excess camber growth