Design of non-ductile steel elements on the seismic overstrength factor

Design of non-ductile steel elements on the seismic overstrength factor

Design of non-ductile steel elements on the seismic overstrength factor

(OP)
Dear experts

For the seismic design category (C ,D & E ),where is the provision/section in the code (ASCE OR AISC) discuss/describe the design of non-ductile elements like connections, base connections, bracing ,…etc., on the overstrength factor.and also is there any exception we can consider to avoid this such factor in the design?

Thank you

Replies continue below

Recommended for you

RE: Design of non-ductile steel elements on the seismic overstrength factor

Overstrength factors are specified by ASCE 7-16 for different systems. ASCE 7 contains building level requirements for application of overstrength, and then reference documents such as ACI 318 and AISC 341 contain lateral system level requirements for application of overstrength.

There are a fairly large number of provisions requiring overstrength, some have exceptions while others do not.

You would do well to understand the AISC 341 and ASCE 7 Ch 12 requirements if undertaking a ductile steel design in SDC C or above.

RE: Design of non-ductile steel elements on the seismic overstrength factor

(OP)
Thank u driftlimiter
Actually i read ASCE 7- chapter12 and AISC341 as well , but i did not find any items speak clearly about the design of brittle elements such as steel connections , base connection , strut , bracing ,..etc.,.
Only section 12.10.2 and the writer speak about the collector elements in the concrete buildings .
It is not clear for concrete.

Thank you

RE: Design of non-ductile steel elements on the seismic overstrength factor

It depends heavily on the selected seismic system. For example Ordinary concentrically braced steel frames system requirements Chapter F Section 4a (1) (i) (AISC 341 V2) says: ... "The forces in braces in tension shall be assumed to be the least of the following: (b) the load effect based upon the amplified seismic load.

The 'amplified seismic load' is nothing more than Overstrength Factor times E. There are many other references therein. Sometimes the language is not consistent.

Following ASCE7 for seismic requires the use of structural systems in table 12.2-1 or alternate approved system. So there isn't general guidance about ' brittle elements'. THere is specific guidance provided for the selected structural system.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close