Current Transformer Thermal Factor
Current Transformer Thermal Factor
(OP)
Hi Gents,
I had a question - is the thermal factor rating on a current transformer refer to continuous or overload capability of an instrument to carry increase in current? For example, if 1000:5 CT has TF of 2.0 at 40 degree C ambient, does this mean that this device can carry 2000Amps continuously at 40 degree constant ambient temperature?
Thank you for clarifying.
EE
I had a question - is the thermal factor rating on a current transformer refer to continuous or overload capability of an instrument to carry increase in current? For example, if 1000:5 CT has TF of 2.0 at 40 degree C ambient, does this mean that this device can carry 2000Amps continuously at 40 degree constant ambient temperature?
Thank you for clarifying.
EE
RE: Current Transformer Thermal Factor
https://www.hyee-current-transformer.com/info/curr...
The short form is that for higher thermal factors, the local ambient must be MUCH lower, because the CT winding total temperature (ambient plus rise) is limited to 85 C.