I have a 16 inches (outside diameter)chilled water pipeline (carbon steel) that is 20 feet long. Water is flowing through it with an initial temp of 1 degC. The line is exposed to an air temperature of 40 DegC and I would like to know the temperature at the end of the pipeline. The flow rate is 2000L/Hr.
I'm trying to generate some kind of pipeline heat gain table using the exposed pipe.
Can anybody helps
I'm trying to generate some kind of pipeline heat gain table using the exposed pipe.
Can anybody helps
RE: Cooling loss
In a 16" pipe? Why. Far too big
Can you check your units and flow?
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Cooling loss
TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm
RE: Cooling loss
This statement is a scenario. You can change flow, dis of pipe. I just want to calculate cool in loss
RE: Cooling loss
RE: Cooling loss
Use your engineering degree. Internal resistance to flow will be the standard convective heat transfer coefficient calculation based on Re and liquid properties. The pipe will, too, will be standard with the metal thickness and material properties.
It's the outside air that presents something not found standard in engineering textbooks. If this pipe is outside, there are usually too many factors to get an accurate number because the conditions change so wildly. If you want to approach this analytically, there is a method for calculating the Reynold's number of a gas flowing on the outsideof a pipe based on wind speed. You would treat this as convective heat transfer, with your thermal boundary layer thickness being dependent on the Re number. Then, you can do your usual Q = U*A*dT, with U being the inverse of the sum of the thermal resistances.
If it rains or if your pipe temperature is below the dewpoint, be prepared for all of the above calculations to wildly underestimate the heat loss.