I have a terrible confusion between the following currents:

-Ith as mentionned in IEC 60909-0:thermal equivalent short-circuit current ,the rms value of a current having the same thermal effect and the same duration as the actual short-circuit current, which may contain a DC component and may subside in time

-Icw as IEC 60947-2: Rated short-time withstand current (Icw),the rated short-time withstand current of a circuit-breaker is the value of short-time withstand current assigned to that circuit-breaker by the manufacturer under the test conditions specified

For a.c., the value of this current is the r.m.s. value of the a.c. component of the prospective short-circuit current, assumed constant during the short-time delay.

Both currents are however subject to a duration (1 second for example)?
Any explanations which can help me?
thanks a lot

RE: Still fighting with Ith and Icw

Dear Mr. 98mlo (Electrical)(OP)30 Jan 23 15:1
" #1. ....-Ith as mentionned in IEC 60909-0:thermal equivalent short-circuit current ,the rms value of a current having the same thermal effect ..... which may contain a DC component and may subside in time....."
In IEC 60909-0 there are two typical curves of short circuit current, i.e. near to or far from gen ....... Take note that the curves are offset due to "A" the initial value of the direct current, which subside in time. The upper envelope 1 and the lower envelope 2 are NOT sinusoidal; due to 3 the decaying direct current.
I am of the opinion that : the Ith concept is to determine the offset into a steady r.m.s. equivalent. . See 2 below.

"#2. ....-Icw as IEC 60947-2: Rated short-time withstand current (Icw).... is the value of short-time withstand current...."
Per IEC 60947-2 states Icw .... is the rated short-time withstand current, for a.c., the value is the r.m.s. value of the a.c. component of the prospective short-circuit current, assumed constant during the short-time delay. The short-time delay shall be.....up to 1 s.

"#3. Both currents are however subject to a duration (1 second for example)?..."
3.1 Per IEC 60909-0 , time is irreverent. See above 1.
3.2 Per IEC 60947-2, short time delay shall be at least 0.05 s, preferred value being 0.05, - 0.1,- 0.25, - 0.5, - 1 s. In addition, the rated short-time withstand current shall be not less than.....
Che Kuan Yau (Singapore)

RE: Still fighting with Ith and Icw

Ith is general for any equipment and speaks of thermal withstand of the conductors used for winding a CT etc.
Whereas, Icw is specifically for the circuit breakers where the short circuit current also (in addition to heating) produces dynamic forces against which the contacts are supposed to remain closed for the specified duration. This applies to Contactors etc. in addition to circuit breakers which are expected to remain latched during faults external to the subject feeder.

RE: Still fighting with Ith and Icw

(OP)
Thank you for your answers.
I have the following comments on your contributions:
@che12345
Regarding your hypothesis:

the Ith concept is to determine the offset into a steady r.m.s. equivalent.
Now according to IEC 60909 the Ith through this equation ith=Ik "sqrt(m+n) shows that the influence of the thermal effect dc(m) of the DC component of the short circuit but also AC are taken into account.


@RRaghunath and @che12345
I understand that if Icw is for circuit breakers, contactors, I deduce that when in a single line diagram (SLD) if I see 50kA/1s marked on a HV or LV switchboard it is for Icw of electrical equipment and that Ith does not exist for this equipment (circuit breaker, contactor).
I also understand that there is necessarily a check to be made: Ensure that the Icw>=Ith (since Ith is relevant for busbars, CT etc...).do you agree?
Also in view of your comment(RRaghunath) can Icw have a relationship with Ip as Icw is the current that produces the electrodynamic forces and also includes the thermal release): we would have Ip(all the switchboard)>Icw(breakers contactor>Ith: does this make sense to you both(even if Ip is not subject to a duration)?

I would like to thank you for your precious information and do not hesitate to correct me if my reasoning is not correct.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close