If a roof member supports a GWB ceiling, should the D*+L deflection limit be L/240 or L/180? I've always assumed L/240 for this, but I have a case in which it matters.
The wording is pretty specific: L/240 for "stucco ceiling" and L/180 for "nonplaster ceiling." Does that mean a GWB ceiling would have an L/180 limit? It isn't "plaster."
*Creep component of the sustained loads per Footnote d.
Advice and especially references would be greatly appreciated!
The wording is pretty specific: L/240 for "stucco ceiling" and L/180 for "nonplaster ceiling." Does that mean a GWB ceiling would have an L/180 limit? It isn't "plaster."
*Creep component of the sustained loads per Footnote d.
Advice and especially references would be greatly appreciated!
RE: IBC Table 1604.3 Roof Member - GWB Ceiling
2) The obvious difference between plaster and GWB is the jointing. However, I don't see that the jointing reliably improves things relative to the plaster case. If you've got an 8' length of GWB located at midspan, it's fasteners will force it into the same curvature there that the plaster would have been forced into.
3) 1+2 = I apply the L/240 to GWB.
The code could probably use a modernization in terms of the materials they list for this stuff.
RE: IBC Table 1604.3 Roof Member - GWB Ceiling
RE: IBC Table 1604.3 Roof Member - GWB Ceiling
It would've been nice if NWCB mentioned L/180!