Insufficient Concrete Cover for bored pile that's already cast

Insufficient Concrete Cover for bored pile that's already cast

Insufficient Concrete Cover for bored pile that's already cast

(OP)
Hi guys,

May you kindly share the experience of how you rectified the low concrete cover of the bored pile that's already cast? The specified concrete cover should be 75mm but it's found less than 30mm at the actual site. To add an additional concrete cover or providing a protective coating on the concrete surfaces is not possible as the bored pile length is 33m below the ground level.

Here is the attached picture.
https://files.engineering.com/getfile.aspx?folder=...

RE: Insufficient Concrete Cover for bored pile that's already cast

There's not much you can do, but evaluate the effects to see if concrete cover is acceptable. You may be able to add some passive cathodic protection.

-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik

RE: Insufficient Concrete Cover for bored pile that's already cast

Sorry... misread the question.

RE: Insufficient Concrete Cover for bored pile that's already cast

I have seen this issue and a second pile was bored nearby. This is a reason not to like the auger-cast piles.

WMA

RE: Insufficient Concrete Cover for bored pile that's already cast

-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik

RE: Insufficient Concrete Cover for bored pile that's already cast

(OP)
@Dik: Thank you for your response. I think CP system is an option to consider. What do you think about leaving the piles as they are if the structural engineers prove that these piles only receive compression loads? Or we can just add another shorter piles alongside to resist any uplift and lateral load effects as only the top portion of the piles need the reinforcing rebars?

@WMArmstrong: Thank you. Adding more piles is supposed to be the last resort.

RE: Insufficient Concrete Cover for bored pile that's already cast

It's not a strength issue, I think. It's a corrosion one. Unless you have fairly large bars, the flexural strength will not be diminished by much based on the cover. Corrosion would be my main issue.

-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik

RE: Insufficient Concrete Cover for bored pile that's already cast

And even if compression only piles, some length of the pile would likely be ignored in terms of confinement of the concrete where it would need to act as a reinforced concrete column. You need the rebar for that.

Doing shorter piles also isn't a good option as those shorter piles will have different performance characteristics. When possible, uniformity in the foundation system is usually important. The project geotech would be a big help here, though, as they may be able to assist in finding an acceptable solution.

RE: Insufficient Concrete Cover for bored pile that's already cast

It depends on the loading and the pile... I've done hundreds of them with a single 15M or #5 bar in the center going into grade beams... for anchor rods, a small 2' 'cage'.

-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik

RE: Insufficient Concrete Cover for bored pile that's already cast

Is the insufficient cover problem along the entire 33m length of the pile?
Is the soil aggressive for corrosion?
Check the capacity of the pile assuming reasonable corrosion reduction in the area of the as-built reinforcing steel?
Jet grout down along the perimeter of the pile?
Install a new pile?

www.PeirceEngineering.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close