Pressure Transducer reporting a negative value

Pressure Transducer reporting a negative value

Pressure Transducer reporting a negative value

(OP)
Hello Gents,
I'm looking at a trend in PI for a water level value and the value is fluctuating below 0 feet and above 0 feet. To me that is strange, I'd expect the trend to be above 0 feet. What can I infer from this trend? When the sensor is reading & reporting a negative value, is that indicative of the sensor issue or perhaps a comms issue?
Any insight on this would be helpful.
Thank you,
EE

RE: Pressure Transducer reporting a negative value

Quote:

When the sensor is reading & reporting a negative value, is that indicative of the sensor issue or perhaps a comms issue?

Only if the comms were so poorly designed that missing or corrupt data didn't get flagged as bad data. Also, given that comms problems are ostensibly random, it would be highly coincidental that your readings are only slightly negative, as opposed to hugely positive or negative.

What does the actual data look like?

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm

RE: Pressure Transducer reporting a negative value

A couple common causes of dither: a calibration issue or electrical noise.

Calibration
Whatever measures the water level is probably some instrument with an analog 4-20mA output. If the transmitter's output is out of calibration slightly, the output signal might be 3.99mA or 3.98mA at zero level. The receiver device correctly interprets anything below 4.00mA as a negative value. Or the receiver might be mis-calibrated so that it interprets 4.00mA as 3.98mA and then reports a negative value.

Electrical noise
The signal wiring can pick up electrical noise which creates a signal that dithers around the nominal value.

Communication issue
The field device that's doing the measurement can communicate to the 'system' by either an analog signal (4-20mA, 0-10V) or over a digital bus, like Profibus, Foundation Fieldbus, Modbus, or a wireless protocol. A digital number communicated over a digital bus can be relied upon to not be corrupted by noise, because digital communication protocols as a rule discard any data with corrupted bit(s).

But the reported digital value is only as good as the analog sensing behind it, and all process measurements start at the analog level. There are a number wireless sensors that cannot be field calibrated, whereas their analog counterparts can be. The 'wireless' bandwagon let all sorts very low end, marginal sensors into the field because of the rush to go wireless and the IIoT (industrial Internet of Things) bandwagon is feeding the cheap-but-wireless-sensor approach.

But in the end, does dither around zero level really matter?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close