Two different current ratings for power cables?

Two different current ratings for power cables?

Two different current ratings for power cables?

(OP)

There seems to be 2 different ratings used for current in power cables. Im not totally sure what the relevance of each is.

Lets look at this cable
Qualtech 313010-01

The datasheet says it is rated for 13Amps
However, there is a table for appropriate currents used for power transmission
https://www.powerstream.com/Wire_Size.htm
according to this, when the wires are bundled, it can only do 2.3/3.6Amps

When do we need to use the standard AWG power transmission rules? Is this for wires that go through UL approval testing? or as the document says, the National Electrical Code.

I realize national electric code is for NFPA 70 and used with it which means in the USA that we need to follow it as OSHA calls this out. So Why are there 2 sets of currents ratings? Im honestly confused by the regulations, any help is appreciated.

RE: Two different current ratings for power cables?

The ampacity of cable depends on ambient temperature, insulation limitations, and installation conditions. The "power transmission" rating in your powerstream link is not a regulation, it is a conservative estimate based on 700 circular mils per amp. For installations covered by the NEC, use the NEC rating if installation conditions are met, derating if necessary for other conditions. The Qualtech cable you referenced is a cord set with a manufacturer's rating. The manufacturer's rating cannot be exceeded.

RE: Two different current ratings for power cables?

In my opinion, if we could speak about "rating" then only the conductor maximum permissible temperature for continue loading-no duration limit-or for short time or for limited time, may be considered rated.
For xlpe insulation, for instance, continue maxim temperature is 90oC, for short time 250 oC and for limited time as "Emergency Overload" 130oC. So, this will be the temperature of the conductor, in contact with this insulation.
The temperature depends on the losses produces in the conductor-proportionally with conductor resistance and the current and the environmental medium temperature. When the conductor losses are evacuated towards the environmental through different layers of insulating material -conductor insulation, jacket, serving, ducts, concrete or air, earth and other, the temperature drops with the multiplication between losses and the thermal resistance of the layer and eventually gets the environmental temperature-air or earth for instance.
Then, the ampacity of a cable is different for exposed in free air, in conduits, on cable trays, outdoor or indoor, underground burry directly, in conduits or ducts, in concreted duct bank and other.
Even, the conductor resistance it is not a constant and depends on material type-copper or aluminum or else, temperature, frequency, number of parallel cable and other.

RE: Two different current ratings for power cables?

You referenced two completely different application listings for wire Amperage and got different numbers. The Qualtech 313010-01 is a power cord, and 16 AWG for use over 6 feet is perfectly fine and typical for a power cord. As jghrist pointed out, the amperage of wire depends upon ambient temperature, insulation limitations, and installation conditions. I would add to that LENGTH (don't want too much voltage drop).

The power transmission reference you used is a guideline for LONG LENGTH applications. A 16 AWG wire has 4.09 Ohms/1000 meters at 25C (increases with temperature). So if you tried to pass 16 Amps through a 1000 meters of 16 AWG wire you would have 65 Volts of line drop. An unacceptable current for 16 AWG power transmission over long distances. But if you passed 2.3 to 3.6 Amps (by the chart) you would have 9.4 to 14.7 Volts of line drop.

Typical example from my area of experience. I design power inverters. I might pass 50 to 70 amps through the lead of a TO-247 MOSFET that is 1/2" long. The MOSFET lead has the copper area equivalent of about 16 AWG wire. But this current is fine for this application.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close