I have an existing condition that I am trying to work out and make work.
Existing single story light framed house. Roof is 4x10 beams spaced @ 7ft o.c. & 2x T&G spans between. See attached picture of the connection between each 4x10 beam at the ridge point.
Architect wants to install 2x10 framing over the top of the existing 2xt&g & 4x10 beams. The new roof will continue up past the ridge line as a shed roof.
(As you look at the picture roof continues up to the right)
This is only a problem at one location in the house(living room) The actual shear is greater then allowable by about a factor of 2.
In order to make this connection work I was considering two 1/4" thick steel plates, one each side of the 4x10 in order to increase the section modulus for greater shear resistance. Any thoughts? I rough sketched the plate on the picture.
Trying to determine how to analyze this. Could I assume that both steel plates cantilever past the support bolt group on the right beam, therefore creating a moment that has to be distributed through the bolts/beam?
Thanks Erik
Existing single story light framed house. Roof is 4x10 beams spaced @ 7ft o.c. & 2x T&G spans between. See attached picture of the connection between each 4x10 beam at the ridge point.
Architect wants to install 2x10 framing over the top of the existing 2xt&g & 4x10 beams. The new roof will continue up past the ridge line as a shed roof.
(As you look at the picture roof continues up to the right)
This is only a problem at one location in the house(living room) The actual shear is greater then allowable by about a factor of 2.
In order to make this connection work I was considering two 1/4" thick steel plates, one each side of the 4x10 in order to increase the section modulus for greater shear resistance. Any thoughts? I rough sketched the plate on the picture.
Trying to determine how to analyze this. Could I assume that both steel plates cantilever past the support bolt group on the right beam, therefore creating a moment that has to be distributed through the bolts/beam?
Thanks Erik
RE: Connection over stressed.
-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates
-Dik
RE: Connection over stressed.
I agree with dik - if timber rivets aren't common where you are and it won't be visible, using many screws would be a good alternative.
RE: Connection over stressed.
Since another layer is being added, place your reinforcement plates on top and bottom, that’s the natural strength of the joint anyway, one big ole scarf!
RE: Connection over stressed.
If the ladder it seems like the segment on the left is already just ignoring the segment on the right and simply bearing on its tiny little toe.
Might consider sucking that crack closed from below with some timberlok screws. Could use them to resist tension and shear if needed.
RE: Connection over stressed.
Can you configure the over-framed portion in a way that makes the issue go away by placing the roof load directly over the beam?
RE: Connection over stressed.