Looking at a proposed electrical design....they've got an SPD connected right at the new switchboard through a branch circuit breaker.
I'm thinking perhaps this just for disconnection means.... but they used a #6 wire on a 100A trip. #6 is too small for a 100A circuit breaker normally. But if it's just just used for disconnection - is this necessarily wrong ? And perhaps it's a tap rule exception, and the HPI cable has a higher ampacity ?
I'm thinking perhaps this just for disconnection means.... but they used a #6 wire on a 100A trip. #6 is too small for a 100A circuit breaker normally. But if it's just just used for disconnection - is this necessarily wrong ? And perhaps it's a tap rule exception, and the HPI cable has a higher ampacity ?