Contact US
Earthing system measurments
Hi experts
The ground system of our (industrical plant) is baised on many ground rods in diffents areas ,that are connected to the same ground network.
using Megger DET24C .
The measurmetns of some rods show relativluuty high grounding resistance (40 to 110 Ohm) .
what is the minium reading and if there any stantrdes for grounding rods
RE: Earthing system measurments
Dear Mr. Emadshaaban1987 (Electrical)(OP)23 Nov 22 12:59
"....#1. The ground system of our (industrical plant) is baised on many ground rods in diffents areas ,that are connected to the same ground network."
This is the usual practice. In numerous cases one or two ground rods may not achieve the resistance required. Therefore with many ground rods planted at different areas which are connected to to the same ground network is a good solution, to achieve the required resistance.
Note: (a) The distance between ground rods shall be as far apart as possible (but NOT closer that say 8m). They may be in any location and any direction.
(b) It is usually better to have numerous ground rods connected together than driving a single or two rods only deeper or increasing the diameter/material of the ground rods.
"... #2. The measurmetns of some rods show relativluuty high grounding resistance (40 to 110 Ohm) .what is the minium reading and if there any stantrdes for grounding rods"
There is NO standard that stipulates the resistance value of the ground rod. It varies as what your measurement shows (40-110 Ohm). This is normal/expected. It shows that some are no good and some are bad!.
Note: To improve/lowering the resistance by
(a)change the location to a (usually) wet area,
(b) drive it deeper but usually need not exceeding say 8m. Any deeper may have limited effect. (c) plant more rods at different directions see #1. would be a better choice.
(d) the total combined resistance that is within your requirement is more important than the individual value.
Che Kuan Yau (Singapore)
Hi che1234, thank you for such details information, this information is really helpful.
https://agnisolar.com/
Click Here to join Eng-Tips and talk with other members! Already a Member? Login
Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now
Close Box
Join Eng-Tips® Today!
Join Us             Close