Problem high MVA import after transformer energisation

Problem high MVA import after transformer energisation

Problem high MVA import after transformer energisation

(OP)
Hi
We have an issue with utility company. We have a high utility bill after we energised our 55 MVA 66 kV/11 kV transfo.
After the high inrush, the stable current was 38.3 A Is this stable current abnormal for a 55 MVA transfo? It is the first time that we have this issue.
What may be the cause of this high MVA consumption? What can be done to prevent this?
Please see attached recording. Thanks

RE: Problem high MVA import after transformer energisation

What does the transformer test report indicate? (% excitation current).

I'm guessing the utility charges a power factor penalty. Consider power factor correction.

RE: Problem high MVA import after transformer energisation

So is the high bill from the KWH, or from the demand?
The transformer should not use much energy for the load it serves.
Maybe the demand is from the equipment you have in service.

RE: Problem high MVA import after transformer energisation

(OP)
We had this issue after annual maintenance when we energised the transformer. There was nearly no load on the plant. We are aware of this issue of high MVA demand. At start up, we atart each big motor after 15 min interval until we are synchronised and start to export MW to the utility grid.

RE: Problem high MVA import after transformer energisation

(OP)
The on load tap changer has 14 positions. If after maintenance, the tap changer was at an extreme position and at the same time the transformer wa energised, can this be the cause of the high MVA import?

RE: Problem high MVA import after transformer energisation

38.3A current when transformer is on no-load is high, considering rated current to be ~480A at 66kV. Could it be that the grid voltage is > 66kV or the transformer tap is below nominal (i.e. towards extreme tap-14) when this measurement was done?
In either case, the transformer is overfluxed causing it to draw higher magnetising current, i.e. drawl of high MVArs from the 66kV grid.
High MVArs (for a given MW) translates in to higher MVA demand.

RE: Problem high MVA import after transformer energisation

You do also know that a high demand will stay on a bill for some time after the peak is set? I think normally a year.

RE: Problem high MVA import after transformer energisation

(OP)
Yes we are aware of this.

RE: Problem high MVA import after transformer energisation

A utility I'm familiar with calculates average pf using the kWh and kVarh during the month. The percentage points below 95 are applied on top of the real 15 min. demand. To ensure the highest possible "billing demand" charge, load your service heavily for 15 minutes then let all transformers idle for the rest of the month.

RE: Problem high MVA import after transformer energisation

(OP)
What can be done to prevent this from happening again? Can we add overfluxing protection in transformer relay?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close