Inverter Drive Setting 4
lukin1977
PY
Hello
I am doing the configuration of a VFD and in the "select control mode" there are 3 options
1. SVC control
2. FVC control
3. V/F control
What are the first 2?
The "VC" in 1 and 2 stands for "vector control". This is closed-loop control of the motor as opposed to the open-loop V/F (voltage/frequency) control of 3.
As to the first letter, different companies use different terminology. "S" is probably for "Space" as "Space Vector Control" is a term often used. "F" may refer to "Flux".
Usually, the biggest difference between different vector control algorithms is whether they use a shaft position sensor or estimate the shaft angle from various electrical properties and a good mathematical model of the motor. You will probably have to consult the VFD mode to see what they are talking about.
Curt Wilson
Omron Delta Tau
It's simulated and full vector control for 1 and 2. Full vector control require a shaft encoder $$$. Modern drives have good torque characteristics in simulated vector but if you're using the drive for a hoist or need best low speed performance you'll still need an encoder.
V/F is volts /frequency. It's the simplest control format but has poor starting torque. It's acceptable for small fan and centrifugal pump applications.
Re-reading that 18 years later, I was reminded of my friend Gunnar (skogsgurra) with whom I collaborated on that. I miss him. RIP.
thanks for your explanations