Hello all. New guy at this so please be kind. Looking at doing a 13d system for a house. Trying to figure out how calf the system with a home tank. I’m looking a flowing 2 sprinklers at the rates GPM needed. I also have a flow test. But do I use the flow test and the pump together? Or do I start calcs at the tank. I’m also trying to figure out what pressure and GPM for the tank system. Like I said I am new at the pump and tank scene. Any help would be greatly appreciated.
RE: NFPA 13d
RE: NFPA 13d
Travis Mack, SET, RME-G,
Ferguson Fire & Fab, dba MFP Design
www.mfpdesign.com
RE: NFPA 13d
HH3 Performance- 350 Gallon Tank
MODEL gpm 0 10 20 30 40 50 60
HH3-200A PSI 67 63 56 50 43 35
HH3-150SP PSI 55 55 52 50 46 40
HH3-150C PSI 48 47 45 43 40
HH3-300A PSI 74 72 65 54 47 41 33
HH3-300C PSI 59 59 58 56 53 50 47
RE: NFPA 13d
Just plug that pump curve into any computer calc system for fire sprinkler systems and you will be good.
Otherwise just look at your pump data there. Pick the flow that is greater than your demand. Then use the corresponding pressure. That is an over-simplified way of doing it.
Travis Mack, SET, RME-G,
Ferguson Fire & Fab, dba MFP Design
www.mfpdesign.com
RE: NFPA 13d
You will need the 350 gallon tank. For the computer calcs, just use the pressure at 0 flow for static and the pressure at 40 gpm for your residual pressures.
Travis Mack, SET, RME-G,
Ferguson Fire & Fab, dba MFP Design
www.mfpdesign.com