What is the purpose of drain valve in fire department connection?

What is the purpose of drain valve in fire department connection?

What is the purpose of drain valve in fire department connection?

(OP)
Can anyone clarify the purpose of drain valve in fire department connection?

RE: What is the purpose of drain valve in fire department connection?

This piece of pipe is supposed to be dry unless used by the ire brigade. So if left without full drainage after use, a small amount of water will be trapped and eventually get frozen. That may clog the connections for future use (in case the next time happens under cold weather).

RE: What is the purpose of drain valve in fire department connection?

(OP)
Thank you UFT12, for the clarification.

The picture shows LPCB approved breeching inlet (Fire department connection). I have not found the similar arrangement in UL listed fire department connection.

Could you please clarify?

RE: What is the purpose of drain valve in fire department connection?

It is depended on the fire brigade and their equipment they use.

A side note, if this equipment is used as dry outlet for roof supply (not on street level for supply), it may also be to allow release of trapped air while the pumper below has connected.

RE: What is the purpose of drain valve in fire department connection?

It could also allow you to drain down the fire hose in a controlled manner once the upstream valve was closed?

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: What is the purpose of drain valve in fire department connection?

And if the check valve leaks the water can drain from the FDC via the automatic ball drip. Big deal in cold climates. Also if the caps on the FDC are tight and the check valve leaks the length of pipe past the check valve will be pressurized. The firefighter maybe injured by the cap when loosing it or taking it off.

From the Automatic Sprinkler System Handbook 2013 Ed.

8.17.2.6* Drainage. The piping between the check valve and the outside hose coupling shall be equipped with an approved automatic drip in areas subject to freezing.

Comment Section on the above.

In the event that the check valve in the Siamese connection leaks, the purpose of the automatic drip is to drain this water to a safe location and to maintain the piping between the check valve and the hose couplings free of water. Without the automatic drip, any collected water could freeze and prevent the fire department from pumping into the system under fire conditions. This automatic drip also facilitates any maintenance of the fire department connection piping, because this portion of the pipe is already free of water. Exhibit 8.62 shows an automatic drain valve used on the fire department connections. The drain should be located at the lowest point of the fire department connection piping to allow complete drainage.


RE: What is the purpose of drain valve in fire department connection?

Interesting code reference from LCREP since NFPA states an "approved AUTOMATIC drip in areas subject to freezing." Seems you could only use that get-up in non-freezing areas. In freezing areas automatic is req'd, which would mean a ball drip which is all we specify anyways.

RE: What is the purpose of drain valve in fire department connection?

I always used my pen to push the ball and make sure it was loose and not stuck closed, either due to trapped pressure, corrosion or debris.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close