Can anyone assist with the technical backing on the sizing of roof vent nozzle for a water tank D=7.4m, H=7.5m

RE: WATER TANK ROOF VENT SIZING

Api 2000?

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: WATER TANK ROOF VENT SIZING

As expected, no mention of any Code of Construction.... or any other significant details

Let the long sad process of getting details from the OP begin !!!

MJCronin
Sr. Process Engineer

RE: WATER TANK ROOF VENT SIZING

Our just make it one size bigger than the biggest pipe coming into or out of it.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: WATER TANK ROOF VENT SIZING

API 2000 gives methods for sizing vents for atmospheric tanks. Basically the method involves two considerations:

1) Vent size must be able to pass input filling or output emptying of liquid at the same rate it flows in the tank or out of the tank and not exceed the tank design pressure which is usually very small on the order of inches of WC or less. Therefore if you take the expected maximum flow in or out of the tank say 1000 gpm and convert to cubic feet per second this is the volume of gas that it must pass in or out without exceeding the positive or vaccuum design pressure. In this case the gas in the tank will be air with saturated water vapor.

2) Since API was developed for oil and gas storage tanks there is also a component of vaporization of the volatile components in the tank. For instance gasoline is very volatile so as the tank is filling or emptying there are vapors generated by the liquid which also adds to the volume that needs to be included in the design flowrate through the vent. However with water in tank I don't think this vaporization amount will matter that much but check API if there are any allowances.

RE: WATER TANK ROOF VENT SIZING

Correction to the above - for case 2 above the correct mechanism for flow out of the tank is when it may be raining and the vapor space cools down simultaneoulsy during withdrawl of liquid which causes additional air flow into the tank due to cooling down and shrinking of vapor above the tank - this will also apply to air with water vapor. Also there is thermal expansion of fluid in tank considerations for outbreathing.

Here is a sample calculation with explanation on the web:


https://chemicalprocessengineering.com/api-tank-br...


RE: WATER TANK ROOF VENT SIZING

For a typical municipal tank with a shop-fabricated vent, just size it as big as the largest inlet or outlet (or combined are if multiple), keep the open screen area similar to that, and it should be good. If you check sizing based on pressures and flow characteristics, it should show as considerably oversized.
For a manufactured vent or P/V vent, get flow curves or data from the manufacturer.
For shop-fabricated vents, ASHRAE has duct-flow data that covers screens, exhaust hoods, etc., and some of that can be applied.

RE: WATER TANK ROOF VENT SIZING

Is this is a potable water tank or a fire water tank? If potable water, making the vent freeze proof for both pressure and vacuum is as important as being sized to relieve pressure and vacuum, and it must have fine mesh screening to exclude bugs and birds.

RE: WATER TANK ROOF VENT SIZING

In addition to the advice above by JStephen, if possible, consider also not desired emptying, as having a discharge opening fully open to e.g to the surroundings. If not restricted by codes and beneficial for the tank roof design, you could consider dividing the required air access opening cross section over multiple vent openings.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close