Pile Embedment - Broms method vs IBC method

Pile Embedment - Broms method vs IBC method

Pile Embedment - Broms method vs IBC method

(OP)
I have been doing some work with a telecom group and I have been asked to review embedment calcs for a light pole with an antenna on top. Normally for something like this, I use the module built into Tekla TEDDS for "flagpole embedment" which uses the IBC method. The designer who sent me his calc used the Broms method from AASHTO's standard on luminaire design. I checked the design using both methods and similar soil parameters. The required embedment using Broms was 8.5 feet, the IBC method was 20 feet. I have been trying to figure out why there is such a discrepancy. Additionally, the pole is 50 feet tall. A good rule of thumb that I've used in the past is to embed the pole 1/3 the height, which would be about 17 feet. Is the IBC method and therefore the rule of thumb incredibly conservative? Or is the Broms method too simplistic to be accurate?
Replies continue below

Recommended for you

RE: Pile Embedment - Broms method vs IBC method

Not having done the sums, but 8.5' for a 50' pole seems a tad light... unless you have really good soil. My SMath calc sheet has 4 or 5 different methods and I select the one that seems to be most appropriate.

So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik

RE: Pile Embedment - Broms method vs IBC method

That said, I do consider Brom's method a higher tier analysis than IBC or h/3 rule of thumb method. Especially if your soil data is reasonable.

----
just call me Lo.

RE: Pile Embedment - Broms method vs IBC method

Quote (buck1017)

...embedment calcs for a light pole with an antenna on top.

Electric utility poles are embedded 10% of pole length plus 2 feet... seven feet for a 50' pole. This includes utility poles with (heavy) transformers on top. Depth of 8.5' seems reasonable for a free-standing pole.

RE: Pile Embedment - Broms method vs IBC method

Double check if either method is assuming restraint at the ground level. It is also common practice to disregard the top few feet from the embedment depth (usually disregard depth equal to foundation diameter).

RE: Pile Embedment - Broms method vs IBC method

Thanks SRE...

So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close