Hello,

During a recent plant visit, I noticed that a Pressure Control Valve (PCV) is installed at the by-pass pipe and not on the main gas line where a globe valve is installed. The pipe is for the gas outlet from a 3-phase crude oil separator.

Can you confirm if this is serviceable from the process/engineering point of view? and whether we have to swap the valves although this job involves a lot of modifications?

Please see the attached photo for reference.

Thanks,

RE: Pressure Control Valve

2
Do you have no one else to ask?

I count six posts so far and counting on what appears to be the same vessel. You could have done it all in one post.

What does the P&ID say?

My guess is that someone did this so that the main bit of the pipe and valve etc was more accessible for maintence.

This ignores the point that manual bypasses of control valves, IMHO, should not be allowed. It looks more like a gate valve, but if it had to be used, is very difficult / impossible to access. Personally I would remove the gate / globe valve and just put in two blind flanges....



Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close