3 ph to 1 ph VFD for a low PF inductive load
4

3 ph to 1 ph VFD for a low PF inductive load

3 ph to 1 ph VFD for a low PF inductive load

(OP)
I have requirement of variable voltage, variable frequency (45 to 65 Hz) single phase testing application where is the load is mostly inductive (0.2 lag typically) and have in mind a 3-phase to 1-phase VFD.

If the 3 phase input is 400 V, 50 Hz, what will be the maximum 1 phase output voltage?

Will the 3 phase input currents be balanced for 1 phase output current?

Since the 1 ph output load is inductive with low PF, will the VFD 3 ph input PF be inductive or close to 1 ?

The 1 ph output current maximum will be 600 Amps. Do 3 to 1 ph VFD's exist in that current rating?

Muthu
www.edison.co.in

RE: 3 ph to 1 ph VFD for a low PF inductive load

The rectifier on the input of the VFD simply passes current from the highest phase voltage. The input side won't see the single phase output. There will not be balance issues.

The maximum bus voltage will be 560v. The maximum output voltage will depend on load.

600 amps is an expensive drive. I wonder if a 3 phase unit could be programmed to fire the gates in parallel so that you would only need to use a 200 amp rated drive?

RE: 3 ph to 1 ph VFD for a low PF inductive load

(OP)
Thank you, tugboateng.

What would be the PF on the input side?

How much output voltage will change with the load?

I am also looking at a Scott connection 3-ph to 1-ph transformer, where I am given to understand the primary current distribution will be 30-30-40%. I would have to put in PF correction caps to reduce that input current. And the frequency cannot be changed, which I can live with.

If the VFD will correct the input PF to about 1, then I can do cost comparison with Scott trafo+PF caps. The whole idea is to reduce the input current.

Muthu
www.edison.co.in

RE: 3 ph to 1 ph VFD for a low PF inductive load

You can not ask what the power factor into a VFD is without defining which one.

Don't forget the power factor is two things. Lead-lag and distortion. The standard lead-lag into a drive is about pf=1.
The distortion power factor can be considerable!

Most VFDs the size you're talking about would freak-out into a single phase load.
Remember also that the output of a VFD is a highly complex PWM signal that looks sort-of like a sinewave because of the inductive aspects of a 3-phase motor. Will this single phase load swallow this?

You might be better served by feeding a transformer with the drive and using only two of the phases out of the transformer.

Keith Cress
kcress - http://www.flaminsystems.com

RE: 3 ph to 1 ph VFD for a low PF inductive load

(OP)
Thanks, Keith.

I should have stressed more on the reduced input current than the unity PF.

If I feed a Wye/Delta transformer via VFD, use only two phases on the Delta side for the inductive load, will the input currents to the VFD be balanced on all three phases and more importantly, will they be low?

Muthu
www.edison.co.in

RE: 3 ph to 1 ph VFD for a low PF inductive load

Many VFD do not allow 2 phase operation (1 phase unconnected)... most VFD enter in error when one motor phase is lost.
Even that some allow (or can choose by parameters to ignore on phase lost), for such current - 600A, may arise other problems.
If input voltage is 3x400V, maximum output is 3x400V, so 400V line to line (between 2 phases).
If you need constant voltage in 45-65Hz range need to programm VFD with base frequency at 45Hz.
Need to check if load allow square wave voltage or close to sinus only (need an output VFD filter), peak voltage tolerated and dv/dt.
If variable freq is not mandatory I think is cheaper and safe is to use a transformer solution.
I tested VFDs with single phase motors but at low power... below 1kW.

RE: 3 ph to 1 ph VFD for a low PF inductive load

(OP)
Thanks, iop.

Not feeding the single phase load directly from the VFD output but via a Y/D transformer. Will that affect VFD input current balance?

The load does not need a sine wave.

Muthu
www.edison.co.in

RE: 3 ph to 1 ph VFD for a low PF inductive load

What voltage do you need? You've only mentioned amperage so far. Based on your description this will perfectly meet your requirements:

https://www.lincolnelectric.com/en/products/le-na-...

For probably 1/4 the cost of an industrial VFD with that rating.

Multi-process welders have both variable current and variable voltage modes controlled with potentiometers. This would be very simple to integrate a remote control to integrate in to your process.

Expect peak output voltage to be around 80V.

RE: 3 ph to 1 ph VFD for a low PF inductive load

Most VFDs have an input rectifier (there are some models that have DC input only, most of them in multi-axis systems).
After rectifier there is a DC bus capacitors bank that feed then 3 phase inverter.
If one phase of inverter remain unconnected and load is inductive type there is no problems with VFD input current balance.
For high inductive load and at such current will be a problem with disconnecting load (high voltage spike)... will be better to reduce voltage from VFD control and then switch off load.

RE: 3 ph to 1 ph VFD for a low PF inductive load

(OP)
The schematic for the proposed system below.

What will be the I1, I2 & I3 and O1, O2 & O3 currents for a single phase 400 V, 600 A, 0.2 PF inductive load on transformer secondary?

Muthu
www.edison.co.in

RE: 3 ph to 1 ph VFD for a low PF inductive load

I'm doubtful that will work, but a VFD is a power conversion device so input currents are always typical of a 6-pulse rectifier with levels matching that required to feed the real power used by the load.

RE: 3 ph to 1 ph VFD for a low PF inductive load

The basic issue ist that a in a single phase load the power fluctuates with 2 x line frequeny while for a symmetrical 3-phase system the power is constant over frequency.

transformer connections can't adress these issue. A Scott transformer can connect connect two identical single-phase loads to a three-phase systemto appear symmetrical, but not a single one. This is the basic challenge of induction heating equipment.

Solutions are:

- Steinmetz circuit(rarely used today due to complex swichgear)
- Inverters with a large energy storage in the DC-link (either an DC-link inductor or a DC-link capacitor)

My former employer manufactures inverters with a suitable topologie for induction heating, but they rarely do inverters at such low power (48 kW). That was the size of our scaled down model to test our controls 20 years ago.

RE: 3 ph to 1 ph VFD for a low PF inductive load

(OP)
Today, I did the inductive load test via a 600 Amps Variac connected to a 400 V, 500 KVA, 695 Amps DG set with the inductive load connected across the two phases of Variac for over an hour.

Inductive load was 345 V, 525 A with 0.3 pf and the measured KW was 54 KW.

Generator current across the two phases was 480 Amps and thankfully it did not kill the machine.

Soon, I plan to repeat the test with a Scott connection trafo with PF correction capacitors on the trafo primary since the VFD method seems complicated and costly.

Thank you all for your time and tips.

electricuwe

This is not a single phase per se. I am just using two phases and the frequency is 50 Hz.

Muthu
www.edison.co.in

RE: 3 ph to 1 ph VFD for a low PF inductive load

Sorry, just recogized that my previous post should read "..constant over time".

edison123, for the power issue it does not matter if a single phase load is connected phase to neutral or phase to phase.

In your case the compensation for sure will help to reduce currents, but don't expect a further improvement by using the Scott-transformer.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close