the relieving load of external fire scenario for distillation collumn

the relieving load of external fire scenario for distillation collumn

the relieving load of external fire scenario for distillation collumn

(OP)
Hi,all,
We all know that the external fire scenario is credible when distillation collumn is located below 25 feet.
But sometimes the distillation collumn is elevated beyond 25 feet with the purpose of avoiding the fire scenario.
So is it needed to consider the relieving load of external fire for the auxiliary pipings of the elevated collumn?
Thank you in advance.

RE: the relieving load of external fire scenario for distillation collumn

I've seen many, not all, distillation columns whose worst case scenario exceeded the fire scenario, like condenser cooling water failure, reboiler tube rupture, or reboiler steam fails wide open. I don't think I've ever seen a column raised 25 feet above grade for the sole purpose of avoiding fire scenario. There were other reasons I've seen columns raised, like maintenance clearance or low bottoms pump NPSH.

Auxiliary piping is not included in fire scenario of distillation column.

Good Luck,
Latexman

RE: the relieving load of external fire scenario for distillation collumn

(OP)
Thank you,Latexman.
I agree with you that the worst overpressure scenario of collumn isn't fire case usually.
But when calculate the relieving load of fire case for distillation collumn it excludes the auxiliary piping no matter what size is the piping?

RE: the relieving load of external fire scenario for distillation collumn

Auxiliary piping is not included in fire scenario of distillation column.

Also, I’ve worked for 3 chemical companies for 43 years. None of them protected piping from fire with a relief device.

That’s another way of looking at it.

Good Luck,
Latexman

RE: the relieving load of external fire scenario for distillation collumn

Quote (phoenixmoca)

So is it needed to consider the relieving load of external fire for the auxiliary pipings of the elevated collumn?
It is user dependent.
API 521-2014
4.4.13.2.2 ... vessel heads protected by support skirts with limited ventilation are normally not included when determining wetted area. The user shall specify whether to include the wetted surface area of connected piping in the wetted-area calculation.

As per my experience piping is not considered in firecase. Note that usually wetted area of piping solely does not contribute enough relief load to exceed max vapor load of distillation column.

RE: the relieving load of external fire scenario for distillation collumn

(OP)
Thank you Latexman.
Would you like to share the another way of think about the fire scenario of piping connecting with collumn?

RE: the relieving load of external fire scenario for distillation collumn

(OP)
Thank you shvet.
As you mentioned Note that usually wetted area of piping solely does not contribute enough relief load to exceed max vapor load of distillation column.
Is there any standard or best practice refers to this?

RE: the relieving load of external fire scenario for distillation collumn

No, there is not. Again - piping is user dependent. For example:

ExxonMobil
The external surface area (not the heat transfer surface area of the tube bundle) of a tower reboiler and its interconnecting piping should be included in the wetted surface of exposed vessels in a fire risk area. The surface area of piping, other than that for reboilers, is not normally included in the wetted surface area.

JGC
Whether the wetted surface area of connected piping is included in the total wetted-area calculation should be determined by respective project

Shell
The impact of attached piping on the vessel’s fire relief load shall be taken into account. The wetted area of piping connected to the equipment that is in the fire zone should be included in the total wetted area of the equipment.

RE: the relieving load of external fire scenario for distillation collumn

(OP)
Hi,shvet,
Thanks a lot for your sharing.
According to the shown company best practices it depends on the user to determine whether the auxiliary piping should be considered.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close