Multi-voltage power system design
2

Multi-voltage power system design

Multi-voltage power system design

(OP)
My prospect is asking me to find the most efficient and cost effective way to supply electricity for various loads with different input voltages.

Primary voltage from utility: 34.5 kV
Load 1 : 1,140 V 3phase
Load 2 : 440 V 3phase
Load 3 : 380 V 3phase
Load 4 : 230 V 3phase
Load 5 : 230 or 220 V 1phase

My plan is to recommend 4 step down transformers:
34.5 kV - 1,140 V
34.5 kV - 440 V
440 V - 380 V, Y
440 V - 230 V, Y

End to end length of the project, which is a tunnel, spans 550 meters long so part of my recommendation is to relocate this whole system every 175 meters so that wires needed will not be too long.

Addition to the engineering challenge is that the prospect is more interested with pole-mounted transformers than pad-mounted possibly due to their price difference. I still believe bias over the other is not yet final specially if I can properly recommend an efficient and cost-effective system.

I know the scheme I imagined can solve the variation of voltage but I'm not quite sure if it is the most efficient one. Also, I feel like there are more economical suggestions than providing 4 transformers. Unfortunately, my existing knowledge and experience can't tell yet.

I am asking for your experience and wisdom. What did you do during the time you experienced same or similar multi voltage requirements?


purpleface

RE: Multi-voltage power system design

You should be able to feed your 380, 230 3p and 230 1p all from the same transformer.

Transformers do catch fire from time to time. Is it good practice to put them inside the tunnel? I think a bank on each end would be safer.

RE: Multi-voltage power system design

Placing 4 sets of 4 transformers sounds pretty strange. How much power is needed at each voltage level? It is often more economical purchase equipment with voltage rates that match the available voltages.

Some folks don't open random hyperlinks, so you get may more responses by editing your post to show your attachment as an image.

Pole mounted transformers use air as the isolating medium. Although have seen them mounted inside of vaults, they take up a huge amount of room due the need to keep people away from the bushings. I had assumed you would need fire resistant transformers in a tunnel, which are typically vault style rather than overhead style.

RE: Multi-voltage power system design

I don’t notice load sizes, but I’d expect dry type transformers rather than oil. But there should be exactly one voltage other than the 34.5kV.

I’ll see your silver lining and raise you two black clouds. - Protection Operations

RE: Multi-voltage power system design

(OP)

Quote (TugboatEng)

You should be able to feed your 380, 230 3p and 230 1p all from the same transformer.

Is it possible to have a single transformer that is capable to provide all of the output mentioned? I don't think so. I would like to ask for a reference/brochure/books/articles that may provide information regarding this specific reply.

Quote (TugboatEng)

Transformers do catch fire from time to time. Is it good practice to put them inside the tunnel? I think a bank on each end would be safer.

I am also thinking to do the same but I'm restricted with the cost. Imagine the cost of having 4 banks on one end and 4 on the other end. Having said that transformers do catch fire, may I know what are other factors that will contribute to this risk except overloading? To minimize risk of catching fire, I already recommended that transformers must be utilized at no more than 80% of its capacity only.


Quote (bacon4life)

It is often more economical purchase equipment with voltage rates that match the available voltages.

There are equipment that was already been used from a different project and will now be brought to use again for this project. For the 1,140V equipment, they said that this is the only voltage rating available from manufacturer.


Quote (bacon4life)

Although have seen them mounted inside of vaults, they take up a huge amount of room due the need to keep people away from the bushings. I had assumed you would need fire resistant transformers in a tunnel, which are typically vault style rather than overhead style.

This is a valuable input! Thanks for this. I now know that the tunnel will be located approx 200m below ground. Installing overhead style underground vs vault/pad-mounted style underground is one of important decision I need to make and there lot of things to consider such as this that I failed to notice. May I ask your more about your experience? What's the advantage of one over the other with respect to this situation?


Quote (davidbeach)

I don’t notice load sizes, but I’d expect dry type transformers rather than oil. But there should be exactly one voltage other than the 34.5kV.

My initial recommendation is pad-mounted, liquid-filled transformers but got immediately turned down because of cost. They are more willing to install-and-relocate the whole system of poles and pole-mounted transformer than to purchase pad-mounted transformers. If I'm going to recommend dry-type transformers, "mobility" will be my reason and most likely be rejected as well due to same reason stated above. Is there any reason to justify this recommendation?

RE: Multi-voltage power system design

Where is this located? This proposed installation sounds quite strange compared to my local practices. Advice from those of us in the USA might not match your local practices.

What sort of tunnel is this? I am having trouble picturing what sort of tunnel as room for 10 meter tall poles, plus additional height for adequate clearance between energize parts and the ceiling.

In the USA, worker safety rules prohibit non-electrically qualified workers from approaching within about 3 meters of an air-insulated power line. Typically a worker with a tools in their hands can reach about 3 meters wide. This means pole mounted equipment needs to be at least 6 meters from any wall/ceiling so that that the is room for future maintenance (i.e. painting, window washing) of the surface. By contrast, cables and padmounted transformers have no clearance requirements.

You would also need separate breakers/fuses for each transformer. Although not hugely expensive, it does add cost, complexity and space requirements. If you do end up having to use multiple transformers, using an autotransformer instead of a regular two winding transformer can be more cost effective for turns ratios of less than 3:1.

RE: Multi-voltage power system design

Some thought from recent tunnel projects:

- It is typical practice to provide all major equipment at the ends of the tunnel. Think about access in emergency situation, it is not easy to get to the middle of a tunnel!

- it is typical practice to provide multiple voltage levels, usually a lower voltage for light & small power services and a higher voltage for mechanical services (jet fans/pumps etc)

- I have never seen so many voltages provided. It is a good idea to look at the loads and the rationale for requesting so many voltage levels.

- Regarding pole-mount vs pad-mount. I suspect whoever is requesting this is not familiar with 'true costs'. Space constraints are at a premium in a tunnel environment, including at the services buildings at either end. The cost of the ancillary requirements will be much more.

RE: Multi-voltage power system design

(OP)

Quote (bacon4life)

Where is this located?

It is located here in the Philippines. Our electrical code was inspired from NEC that's why we have no issues on taking expert opinions from you guys if we are talking electrical matters.

Quote (bacon4life)

In the USA, worker safety rules prohibit non-electrically qualified workers from approaching within about 3 meters of an air-insulated power line. Typically a worker with a tools in their hands can reach about 3 meters wide. This means pole mounted equipment needs to be at least 6 meters from any wall/ceiling so that that the is room for future maintenance (i.e. painting, window washing) of the surface. By contrast, cables and padmounted transformers have no clearance requirements.

May I know what safety standard are you talking about? I will do the reading regarding that. On my end, I will check our worker safety rules as well. Thanks for this :)

Quote (bacon4life)

using an autotransformer instead of a regular two winding transformer can be more cost effective for turns ratios of less than 3:1.

I've never experienced recommending autotransformer. This is an eye opener! Something I need to verify by asking quote from local manufacturer.

Quote (JezNZ)

I have never seen so many voltages provided. It is a good idea to look at the loads and the rationale for requesting so many voltage levels.

It's my first time to handle many voltage levels and it's the reason I ask your expertise. 1,140V is for specific machine with no other option. 380V is for large industrial fans, 440V is for china-made 3phase motors - these equipment were already purchased by the client. 230V 3phase and 1phase are for utility equipment and use. I hate to say this but I don't think I have a choice to change this variety of voltage levels. I need to overcome this challenge as it is.

Quote (JezNZ)

Space constraints are at a premium in a tunnel environment, including at the services buildings at either end

This specific sentence is a game changer! I have already discussed the importance of space but you described it wayyyy better than mine. I will borrow this sentence and tell them on the next meeting.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close