Why can't i get a mili Amp mA value from this leveltransmitter
Why can't i get a mili Amp mA value from this leveltransmitter
(OP)

I am writing from Nigeria i am an electrical engineer, a fresher, I had a challenge yesterday with this level transmitter I wanted to check if it was working so I connected the transmitter in series with my multimeter after which I set to mA on the multimeter I was expecting it to display a value as I deep the sensor into the water but yet I didn't get any value other than 0000 and when i measured the voltage there was 24V DC
RE: Why can't i get a mili Amp mA value from this leveltransmitter
RE: Why can't i get a mili Amp mA value from this leveltransmitter
TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm
RE: Why can't i get a mili Amp mA value from this leveltransmitter
Have you got a model number for this?
RE: Why can't i get a mili Amp mA value from this leveltransmitter
I first thought he was using this to read the sensor directly and didn't apply the loop voltage, just the voltage to power the sensor, but when he mentioned series connection I thought that might not be the case.
A model number for the sensor would be a big help; maybe he will call in again.
RE: Why can't i get a mili Amp mA value from this leveltransmitter
Is it a 2-wire loop powered transmitter?
Or is a 3-wire voltage output transmitter?
How do you know the output is 4-20mA and not Profibus, Foundation Fieldbus or Modbus?
If you have powered a 2-wire loop powered transmitter properly and connected the millammeter properly, then the device is not working properly because a 4-20mA loop powered transmitter never goes 0mA. It might fault low at 3.6mA, it might indicate a below zero (eng units) level at 3.9mA, but a 2-wire loop powered transmitter uses 3.5mA of the loop current to operate so it can NEVER have less than 3.5mA if it's working properly.
RE: Why can't i get a mili Amp mA value from this leveltransmitter
In series with WHAT, though? He made no mention of a receiver, so it's likely the transmitter detected a dead short, in which case I could see it shutting off the output altogether
TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm
RE: Why can't i get a mili Amp mA value from this leveltransmitter
Actually I didn't get a timely response from this group, anyway regarding the transmitter I posted the other day, I discovered when I opened the back the terminal A and B were not connected to the electronic circuit, it was the test point A+and A- that was connected and the PLC was wired in a way that the blue cable was positive and red negative (0) so after changing the connection to the right terminal and reversing the connection that is red to A- and blue to A+ I started to get value on the transmitter, we have called expert to come do the calibration... And regarding the length of the probe,it is a level transmitter and it is used for a tank not up to 1 metre so I guess that is why the cable is short...
Thank you for your time, input and understanding...
Like I said earlier I am a fresher I want to grow I want to learn mostly instrument and automation, please guide me in the best way you can.
Thank you once more lot of love from Nigeria.