Why can't i get a mili Amp mA value from this leveltransmitter

Why can't i get a mili Amp mA value from this leveltransmitter

Why can't i get a mili Amp mA value from this leveltransmitter

(OP)
Good evening sirs and Ma,
I am writing from Nigeria i am an electrical engineer, a fresher, I had a challenge yesterday with this level transmitter I wanted to check if it was working so I connected the transmitter in series with my multimeter after which I set to mA on the multimeter I was expecting it to display a value as I deep the sensor into the water but yet I didn't get any value other than 0000 and when i measured the voltage there was 24V DC

RE: Why can't i get a mili Amp mA value from this leveltransmitter

(OP)
please I also tried using a clamp meter it didn't work, please is there any way else I can test if this device is working or not, thank you I really appreciate your contributions to and suggestions.

RE: Why can't i get a mili Amp mA value from this leveltransmitter

Your DMM's input impedance is too low for a current loop measurement. You need to properly terminate the current loop to measure the correct current.

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm

RE: Why can't i get a mili Amp mA value from this leveltransmitter

Is that even a pressure transducer or is it an ultrasonic transducer? If pressure it's cable length is absurd.

Have you got a model number for this?

RE: Why can't i get a mili Amp mA value from this leveltransmitter

IRstuff - he wrote that he has this in series, so shouldn't the impedance of the meter be low?

I first thought he was using this to read the sensor directly and didn't apply the loop voltage, just the voltage to power the sensor, but when he mentioned series connection I thought that might not be the case.

A model number for the sensor would be a big help; maybe he will call in again.

RE: Why can't i get a mili Amp mA value from this leveltransmitter

A photo of a housing with a probe does not identify what technology or what type of transmitter is involved.

Is it a 2-wire loop powered transmitter?
Or is a 3-wire voltage output transmitter?
How do you know the output is 4-20mA and not Profibus, Foundation Fieldbus or Modbus?

If you have powered a 2-wire loop powered transmitter properly and connected the millammeter properly, then the device is not working properly because a 4-20mA loop powered transmitter never goes 0mA. It might fault low at 3.6mA, it might indicate a below zero (eng units) level at 3.9mA, but a 2-wire loop powered transmitter uses 3.5mA of the loop current to operate so it can NEVER have less than 3.5mA if it's working properly.

RE: Why can't i get a mili Amp mA value from this leveltransmitter

Quote:

IRstuff - he wrote that he has this in series, so shouldn't the impedance of the meter be low?

In series with WHAT, though? He made no mention of a receiver, so it's likely the transmitter detected a dead short, in which case I could see it shutting off the output altogether

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm

RE: Why can't i get a mili Amp mA value from this leveltransmitter

(OP)
Hi guys good evening from Nigeria,
Actually I didn't get a timely response from this group, anyway regarding the transmitter I posted the other day, I discovered when I opened the back the terminal A and B were not connected to the electronic circuit, it was the test point A+and A- that was connected and the PLC was wired in a way that the blue cable was positive and red negative (0) so after changing the connection to the right terminal and reversing the connection that is red to A- and blue to A+ I started to get value on the transmitter, we have called expert to come do the calibration... And regarding the length of the probe,it is a level transmitter and it is used for a tank not up to 1 metre so I guess that is why the cable is short...

Thank you for your time, input and understanding...

Like I said earlier I am a fresher I want to grow I want to learn mostly instrument and automation, please guide me in the best way you can.

Thank you once more lot of love from Nigeria.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close