Grounding CTs and PTs

Grounding CTs and PTs

Grounding CTs and PTs

(OP)
I have an installation where CTs and PTs are installed, but will not be used (not wired for metering nor protection). We will be connecting all phase CT terminals to ground to avoid an open CT situation, but the field contractor wants to also ground phase PT terminals. Is that typical? Those terminals will be reading 120V, so would grounding them cause damage?

RE: Grounding CTs and PTs

One secondary PT terminal should be grounded, but not both. Connect the three in wye and ground the wye point and you'll be good. If you don't ground you risk that secondary voltage float up toward phase voltage due to capacitive coupling across the windings.

Ideally the CTs would have all terminals shorted together and then a single ground from that.

I’ll see your silver lining and raise you two black clouds. - Protection Operations

RE: Grounding CTs and PTs

(OP)
Thanks davidbeach. See attached file for actual PT configuration. This has dual secondary windings (Y and Delta) as you see. So, you're saying for the Y secondary, I connect A1X11, B1X11, and C1XII together, and ground middle wye point only correct? What about the delta winding?

RE: Grounding CTs and PTs

The ground shown on the delta winding is necessary.

I’ll see your silver lining and raise you two black clouds. - Protection Operations

RE: Grounding CTs and PTs

But add a ground to the neutral point of the wye connected secondary.

RE: Grounding CTs and PTs

Mila2015,
"So, you're saying for the Y secondary, I connect A1X11, B1X11, and C1XII together, and ground middle wye point only correct? What about the delta winding?" -
No, for star winding, you shouldn't connect A1X11, B1X11 and C1X11 together. Leave them open as they are. ust connect the star point of PT Y-secondary windings to earth.
Regarding Delta secondary, one of the terminals of broken delta is already connected to earth and that is adequate.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close