How much pressure is required by an exhaust fan when it exhausts straight up?

How much pressure is required by an exhaust fan when it exhausts straight up?

How much pressure is required by an exhaust fan when it exhausts straight up?

(OP)
I'm sure this is simple and I'm not sure why I'm having such a hard time figuring it out. I have an exhaust fan I'm trying to size and it pretty much exhausts into vertical duct 30 ft straight up. I'm pretty sure it's negligible but I can't figure out the calculation for how much extra pressure needs to be exerted due to the vertical column of air. At first I calculated it using the weight of the column of air which is .0807 lbs per cubic foot. My duct is 12x12 so I would just multiply that by 30 ft to get 2.421 lbs. Then the outlet of my fan is 4" Ø so I get 0.193 psi which equates to over 5 inches of water column which can't be correct. Please help this confused man.

RE: How much pressure is required by an exhaust fan when it exhausts straight up?

(OP)
Actually, would it be the difference in air pressure between the room where the exhaust fan is taking air from and the roof where it is exhausting to? That comes out to be more reasonable, more like 0.3 inches but still seems high.
And if I do 70 °F intake and 0 ° outdoor, it comes out to 8 in w.c. so I'm back to being confused.

RE: How much pressure is required by an exhaust fan when it exhausts straight up?

loss is velocity dependent, without knowing that this is all I can offer

Consider:
  • Differential pressure inside to outside
  • Inlet loss
  • Duct friction
  • Regain from 4" round to 12x12 rectangular duct
  • more duct friction
  • Exit loss

RE: How much pressure is required by an exhaust fan when it exhausts straight up?

Hi.. Density change in air with 30 feet height is insignificant and change in pressure due to this 30 feet altitude is also insignificant. You can ignore it in case of air. Just calculate the duct+fittings losses and safety margin of 15% and proceed further.

RE: How much pressure is required by an exhaust fan when it exhausts straight up?

Calculating on the exhaust discharge side is barely any different than on the suction inlet side

You do your normal calculation and fitting loss lookups based on your exhaust airflow, and the duct size and velocity the air is traveling through.

You also may have to account for velocity pressure if you are narrowing/squeezing the duct after the fan exit you need to account for that exit velocity increase. The fan itself should be coming with enough pressure for it’s specific velocity pressure associated with its outlet size but not more.

30’ of height in a building with typical operating pressure wouldn’t even factor in very much. If you want to get into the details, this link will probably help.

https://www.aldes-na.com/wp-content/uploads/2021/0...

And finally see if the fan selection performance has factored in a ducted discharge, sometimes fan manufacturers can account for that and it re-rates the performance you’ll get.

RE: How much pressure is required by an exhaust fan when it exhausts straight up?

(OP)
Thank you, I'll read through that.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close