Flow control of cooling water of heat exchanger
Dear all. Hello.
Why in most industrial plants, cooling water vlave of heat exchabger is manual (non control valve)?
I think we can conserve lots of e energy using regilation of cooling water flow through heat exchanger in different plant load
RE: Flow control of cooling water of heat exchanger
Cooling water systems are a utility that is normally better off running at a constant flow.
Yes, the thermal load changes but not the flow.
Lower flows can be difficult, leading to silting and fouling, minimizing distribution of inhibitors, and requiring more sophisticated pump controls.
Power costs for cooling water circulation might become significant if the HX works at low load for extended periods.
Then maybe introduce a small recirc pump (low head) to recirc say 50% of cooling flow around the HX to reduce the main cooling water pumps. All depends.
Pay attention about your statement on economy energy by reducing the cooling water flowrate (control valve) , this is going to increase the precipitation of salt over the tubes of HX . In other words this is the best way to have a plant collapsing .
Please let you study the chemistry of water and you will understand my comments , in particular study the Langelier and Rysnar saturation indexes.
If you want to save some energy you may adjust the RPM of fans on cooling towers but you need to equip them with VSD .
Good luck
Pierre