Bridging/bracing an overnotched joist- calculations
Bridging/bracing an overnotched joist- calculations
(OP)
Hello, I have a floor joist with an enormous notch on it- much larger that acceptable.
Naturally the corrective course of action is to replace it, however I'm curious to determine if bridging this notch is a viable solution. Based on the notch location, the bridge would need to replace the tensile strength lost by this notch (it is above the centroid near a support). Intuitively, I assume that the volume of this notch is pertinent, but I'm unsure how this relates to a potential solution. Any insight would be appreciated.
Naturally the corrective course of action is to replace it, however I'm curious to determine if bridging this notch is a viable solution. Based on the notch location, the bridge would need to replace the tensile strength lost by this notch (it is above the centroid near a support). Intuitively, I assume that the volume of this notch is pertinent, but I'm unsure how this relates to a potential solution. Any insight would be appreciated.
RE: Bridging/bracing an overnotched joist- calculations
Nobody here can say much without more information! If you provide the following we would be in much better shape to provide guidance:
1. What is the approximate size of the notch (area, perimeter, shape)
2. Where is the notch located relative to the support, and load on the joist (e.g. right underneath a line load above, middle of the room, etc). What are the loads on the floor generally?
3. What's below the joist and in the room (e.g. are we dealing with a finished area, mechanical room, etc). Basically, what access are we looking at?
4. When you say joist that could be anything. What are the specifications of the joist (e.g. 2x8, TGI, etc)
5. What is the spacing of the joists for the floor we are looking at
6. Pictures and/or sketches would also be superb
Those should get us rolling. Also, are you sure the notch is in the tension part of the joist? Most residential joists are single span so a notch above the neutral axis would be in compression in that case. If it's continuous over multiple supports it would be in tension or if for some odd reason you had fixed connections. Could you clarify on that?
RE: Bridging/bracing an overnotched joist- calculations
Firstly, you are correct that this notched would be in compression, not tension- shows how long it's been since I've thought about beam deflection. Regarding the rest of your questions:
- The joists, being extremely old, are 2-1/8" x 7-3/4". Unsure of the species, house is ~100 years old in Ontario Canada.
- The notch is 9" long and 5" deep, starting about 6" off the support.
- Joist spacing is 16" OC
- Finished kitchen is below this joist.
- Room will be a bathroom (notch was done by previous owners to fit plumbing). Currently room is demolished and cleaned- just joists and studs (and old plumbing, but that will probably go).
I had a structural engineer come in to take a look and he told me to replace the joist- he would not elaborate on what calculations he performed to determine the joist must be replaced (I see this is a common point of contention). Completely understandable from a liability perspective, and while it is my most likely course of action, I would still like to know exactly how to determine that this joist is not acceptable.RE: Bridging/bracing an overnotched joist- calculations
RE: Bridging/bracing an overnotched joist- calculations
Rather than think climate change and the corona virus as science, think of it as the wrath of God. Do you feel any better?
-Dik
RE: Bridging/bracing an overnotched joist- calculations
There is nothing preventing me from replacing this joist, would just like to do the math myself.
RE: Bridging/bracing an overnotched joist- calculations
Rather than think climate change and the corona virus as science, think of it as the wrath of God. Do you feel any better?
-Dik
RE: Bridging/bracing an overnotched joist- calculations
RE: Bridging/bracing an overnotched joist- calculations
Depending on the age of the residence, there were a few books from the early 1900s for wood design. But really, 1500psi is a conservative allowable bending stress value for any lumber from that era. I can dig up a reference for you, but not until likely next week as I'm working from home and all of our old reference books from that era are in the office library.
I really feel that the shear calculation of the remaining section will not calculate out. I can't imagine a 2 3/4" x 2 1/8" piece of lumber having almost any shear capacity.
For design of the replacement joist, you could essentially just pick one out of the part 9 span tables as long as there's no bearing walls in the middle of the joists or anything like that. Alternately, ForteWeb is a free program that will also design commodity lumber. Lastly, if you really want to know the ins and outs of the design, you'll want to look at CSA O86 and the CWC Wood Design Manual chapter 2. Should have everything you need in there.
RE: Bridging/bracing an overnotched joist- calculations
As far as shear... If necessary, I'd put a couple of small blocks or steel angles in place and put diagonal comapression members to adjacent members and use a steel strap to take care of the force. It's not likely a 'real' design, but will likely be suitable for residential construction.
Rather than think climate change and the corona virus as science, think of it as the wrath of God. Do you feel any better?
-Dik