IEE519 and IEC6000
(OP)
hello what is the difference between the two standard? is it same?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Contact USThanks. We have received your request and will respond promptly. Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting Guidelines |
|
Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.
Here's Why Members Love Eng-Tips Forums:
Register now while it's still free!
Already a member? Close this window and log in.
RE: IEE519 and IEC6000
- There is no IEC 6000 --> IEC standards tend to have a 5 digit number starting with a 6, like 6XXXX, many of them with different parts
- IEEE 519 is dealing with harmonic currents converters are injecting into the grid up to highest power levels
- There are some IEC standards addressing the same topic, but only at moderate power level, several parts of the IEC 61000 series At higher power level conditions are subject to negotiations between customer and utility
- The methods and the outcome is different
For a reasonable discussion you have to be more precise and more specific.