Hi all,
Designing a stairwell pressurized with the use of NFPA 92A, there is this table which represents the Leakage Areas of buildings. I particulary appraciate the fact that reference are presented, but I have a question: how can I say if a wall is tight average or loose? Is the choice of loose wall always a safe assumption? I am afraid that assuming a wall too loose can lead to a flow rate that when the doors are closed can bring to pressure difference that does not allow to open the doors. I don't know in my geographic area people that are expert about stairwell pressurization, so I hope that someone can give me some hints.
I doubt you will find better guidance on this than your own judgment.
Loose should be used for old buildings or when you know/feel the walls/floors are of pure quality.
Tight should be used for good quality build, heavy duty concrete or areas in basements etc.
Average should be used for anything in between or when you feel that a tight building through time may end up "average".
All in all, unless you have an indication or strong belief for a specific category, average is a good starting point and see what do you get out of it.
Side note, if by any chance you can find a paper of the work done by the references cited, maybe you could find better explanations about those three categories.
I asked this because I was wandering if someone perform test such as doorfan test in the stairwell before the design. I was wandering if it is a best practice
Red Flag Submitted
Thank you for helping keep Eng-Tips Forums free from inappropriate posts. The Eng-Tips staff will check this out and take appropriate action.
Reply To This Thread
Posting in the Eng-Tips forums is a member-only feature.
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Metal 3D printing has rapidly emerged as a key technology in modern design and manufacturing, so it’s critical educational institutions include it in their curricula to avoid leaving students at a disadvantage as they enter the workforce. Download Now
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now
RE: NFPA 92A area leakage
Loose should be used for old buildings or when you know/feel the walls/floors are of pure quality.
Tight should be used for good quality build, heavy duty concrete or areas in basements etc.
Average should be used for anything in between or when you feel that a tight building through time may end up "average".
All in all, unless you have an indication or strong belief for a specific category, average is a good starting point and see what do you get out of it.
Side note, if by any chance you can find a paper of the work done by the references cited, maybe you could find better explanations about those three categories.
RE: NFPA 92A area leakage