Sense Check Me
I need to design a slab-on-grade that can withstand 4 outrigger loads from a 130t mobile crane. I've designed a fair few crane pads on compacted gravel, but never a permanent concrete area.
So far I've got spreader mats under each outriggers to spread the (huge!) point loads. I've checked the rc slab for punching shear and taken load spread at 1:1 down into the underlying sub-grade for bearing capacity checks. For good measure I've also checked spanning for local depressions (future voids) under the slab.
Now, a few thoughts I've got. I conferred with snr colleagues and they reckon the ground is very good (its 1m thick well compacted imported fill) so the ground directly under the outriggers pads is more likely to behave as rigid and the whole area unlikely to act in flexure between the outriggers.
I've been requested to keep the slab 200mm (8") thick. I've added bottom rebar for the punching shear, and top rebar to control shrinkage cracking (but with control joints located between the 4 outriggers).
Does the approach sound sound? Or am I missing fundamentals like spring stiffness and ignoring the slab could acting in bending. Welcome your thoughts.
I can try and upload a sketch if it helps