Short Circuit test on Sync Generator.

Short Circuit test on Sync Generator.

Short Circuit test on Sync Generator.

(OP)
I have a question regarding the short circuit test that is done on generators. While performing the short circuit test, we short the phases, I want know why doesn't it destroy the generator, we are literally creating a three phase bolted short circuit.

RE: Short Circuit test on Sync Generator.

You manually control the excitation so that the output voltage is very low.

RE: Short Circuit test on Sync Generator.

waross or catserveng would be able to confirm this as I've never actually done it, but I understand same technique can be used to dry out alternators. From what I can gather: short the windings, slowly adjust excitation so that desired current is flowing, and periodically shut down and take insulation resistance readings. The I2R heats the windings and slowly dries them out.

EDMS Australia

RE: Short Circuit test on Sync Generator.

Take a look at this link,
https://www.theengineeringknowledge.com/open-circu...

I have done a similar technique on several generators in the field to dry out windings after a field cleaning, but in those cases we only applied enough field current to get the windings warm. The procedure used is pretty much how Freddy has described it above.

Hope that helps, MikeL.

RE: Short Circuit test on Sync Generator.

Generator standards ((IEC etc) require them to be designed and constructed to withstand a sudden three phase short circuit across the generator terminals.

This is the worst case they will see in service as downstream faults will not be as severa as the fault current will be limited by system impedance.

This test is not performed on every generator manufactured as it is stressful and takes time to arrange. It is not a test normally performed in the field.

The decrement curve of current decay can be used to determine generator reactance (sub-transient, transient etc)

RE: Short Circuit test on Sync Generator.

(OP)
Thank you very much everyone for your valuable responses.
Much Appreciated.

RE: Short Circuit test on Sync Generator.

The one time I saw this test done, people forgot that oil was used on something during the rewinding. So the heat of the test caused the oil to smoke out.
Some people very nervous.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close