To answer your question think of the mass continuity of the fluid traveling from one pass to another pass and of the head loss entering and leaving the 1st, 2nd 3rd, etc...pass. As the fluid enters and leave each pass it will either loose temperature( such as in firetube boilers) or gain temperature( such as in a hot water heat exchangers). The designers of these systems will then apportion a certain number of tubes for each pass based the mass rate thru each pass which will remain the same as there will be a change in temperature which changes the density of the fluid decreasing or increasing the volumetric rates of these fluids. In fire tube boilers and hot water heat exchangers the head losses thru each pass will also be nearly the same in each pass. Do hand calculations for the system in your OP to verify.