Eddy Current Drive Issues

Eddy Current Drive Issues

Eddy Current Drive Issues

(OP)
Good day, I work at a Wastewater Treatment Plant (WWTP) where we have 3-25HP Induction motors equipped with eddy current drives on vertical centrifugal solids handling pumps. See motor specs below this post. One motor is starting but there is no output.. pump shaft is not turning until motor is switched off, then it turns slowly and comes to a stop. The second motor is starting but there is no variation in pump speed/output even when the clutch coil is disconnected. Can anyone shed some light on why this may be happening and what troubleshooting measures we can use to find and resolve the problem?

Hoping to hear from you soon.

Variable Speed Drive:
Model AT-320258-0190
Min. RPM 50
H.P 25
Volts D.C 90
Ohms @ 20oC 20.8
Amps Hot 3.46
Max. RPM 805
H.P Diss. 45

INDUCTION MOTOR:
Model 040-092600-0252
Design B
Frame 324TDZ
Hertz 60
Insulation Class B
R.P.M 870
H.P 25
Volts 460
Ohms 20.8
Amps 41
Service Factor 1.15
Code G
Type TEFC
Frame 3
C Max Ambient 40
Replies continue below

Recommended for you

RE: Eddy Current Drive Issues

Sounds like the controls for your EC drives are bad.
You should be able to take some basic measurements and see if they are energizing and changing with input variations.
Reach out to someone who supplies and services these.

= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, consulting work welcomed

RE: Eddy Current Drive Issues

I concur with Ed. about basic troubleshooting, your problem could be as simple as servicing the brushes for the rotating field. Your O&M manual will provide some guidance.
If you do not have one, this Dynamatic manual has the basic information https://www.dynamatic.com/wp-content/uploads/2018/...

RE: Eddy Current Drive Issues

(OP)
Thanks guys. Found the AT Series Manual at Dynamatic.com. We are troubleshooting the control system first. Will let you know how things turn out.

RE: Eddy Current Drive Issues

The OP states, "...vertical centrifugal solids handling pumps..."
It's unclear to the reader if the Eddy Current units are also mounted vertically.
Assuming they are, page 24 in the AT line PDF in the Final Mounting paragraph reads; "...make sure unit is level..."

PDF Reference: https://www.dynamatic.com/wp-content/uploads/2019/...

Not saying the units cannot be mounted vertically, "but" having worked on quite a few of these beasts before most of them disappeared,
I never came across one mounted in a vertical arrangement.

Most of these units have cylindrical roller bearings in them which restricts their mounting to a traditional horizontal arrangement.

Larger Electric Machinery eddy current drives... rated in many hundreds of horsepower are constructed specifically for vertical mounting... so there are vertical units out there.

John

RE: Eddy Current Drive Issues

problem is with EC drivers or it is mounted vertically, it should be rated in hundred od horse power

RE: Eddy Current Drive Issues

(OP)
The eddy current drives are vertically mounted but they were specially modified for this application. Got onto Dynamatic. They were helpful but we haven't resolved the problem yet.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close