Anti static dissipative floor
Anti static dissipative floor
(OP)
Hi, I'm looking for some hours for a clear information regarding the grounding grid bellow the conductive epoxi.
I cannot assure what is the recomendation do someone knows if there is a spacing requirement for the copper strips?
I saw some conflicting information.
Stantard for explosive areas JSP 482 MOD Explosives Regulations
Bonding strips with a spacing of approx 600 mm, shall be laid on the
subfloor under and in intimate electrical contact with the antistatic or conductive floor
covering.
Some others informations from suppliers says one strip for at least an area of 1000 sq ft
Can someone share some experience regarding this? The local is a paint warehouse, condcutive will be 5x10^6 to 5x10^9.
I cannot assure what is the recomendation do someone knows if there is a spacing requirement for the copper strips?
I saw some conflicting information.
Stantard for explosive areas JSP 482 MOD Explosives Regulations
Bonding strips with a spacing of approx 600 mm, shall be laid on the
subfloor under and in intimate electrical contact with the antistatic or conductive floor
covering.
Some others informations from suppliers says one strip for at least an area of 1000 sq ft
Can someone share some experience regarding this? The local is a paint warehouse, condcutive will be 5x10^6 to 5x10^9.
RE: Anti static dissipative floor
TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm
RE: Anti static dissipative floor
You need to know if you need conductivity or static dissipation, or both.
And you need to know exactly how to measure them.
I would expect any coating contractor to have references and have copies of all of the test data from them.
When this done correctly it looks easy, but it isn't.
= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, consulting work welcomed
RE: Anti static dissipative floor
As said by you guys I`ll contact and specialized contractor and request to remove all existing paint and to keep the measurements in the 1 M OHM range (Last measurements from factory install).