Expansion Joints in Big Box Buildings 2
dengebre
We have a single-story “big box” project in Florida that is 480’ x 160’. It was originally an all-steel building, with steel stud exterior walls, and using the Thermal Program (steeltools.org) it shows that an expansion joint is not required (Delta-T = 55 degrees). The project has changed to concrete masonry exterior walls and we are concerned that the restraint of the walls may now require an expansion joint. However, I recently went to my local Walmart Superstore (similar footprint) and they did not use an expansion joint. Are we being overly cautious?
In 480' I would put a minimum of one expansion joint in the long dimension; I typically use about 250'-300' as a max length.
I don't know if it's codified; it's what I do.
Thanks, dold... good link.
The Thermal program by Tomanovich is what I used, but my understanding is that it pertains to all-steel buildings only. I am still baffled as to how the Walmart Superstore down the street is the same size building and has no expansion joint.
Does the Walmart building have masonry control joints? Not the same as a global expansion joint. Detailing of an expansion joint depends largely on the type of framing. If the building consists of rigid frames, you just need to provide a frame each side of the joint. If you are depending on a roof horizontal truss/diaphragm, then the problem is more complex.
they should be at about 30' spacing...
Here is a great article on expansion joints and includes other building materials as well: Link
Also, I'm not sure if you have ever calculated the forces generated from thermal expansion of say a steel beam, but they are crazy high; without allowing for some movement, I expect you would see some issues over time in a building that long without expansion joints.
I've never spliced bridging... I've always terminated it and used X-bridging in the adjacent panels.