Structural steel Transfer Trusses : Deflection limit

Structural steel Transfer Trusses : Deflection limit

Structural steel Transfer Trusses : Deflection limit

(OP)
Dear All
We are designing a steel Transfer truss which supports a floor above. We have limited the Live load deflection as L/600 and Total deflection as L/400.
During the discussion the client representative is saying L/1000 is required that for Total load. According to me , Total load deflection =L/1000 is too
stringent. I would like to know more about the best practice in the steel world.

Regards
Siddha

RE: Structural steel Transfer Trusses : Deflection limit

I don't know what the best practice is, but I would do the following in general:

1. Camber to counteract almost all of the dead load deflection. Only the structure weight in this calculation. If this deflection is very small, then forget the camber.

2. Limit the deflection due to superimposed dead loads plus live loads to avoid violating floor levelness requirements.

3. Limit the live load deflection. By the IBC, this must not exceed L/360, but that seems too lenient for a transfer truss. I don't have a solid reason for it, but your L/600 seems like a good limit.

You might check out AISC Design Guide 3 to see if it includes help for this.

The client's L/1000 limit might be your best friend on this. Transfer trusses and girders can keep an engineer up at night. It's very nice when the truss or girder is controlled - by a wide margin - by something that wouldn't cause collapse. LOL.

Also, imagine if they're saying you need L/1000 and you use a more lenient limit, and something goes wrong. Something is out of level, a finish cracks, you name it. Even if the problem is not caused by your design, that might be hard to prove. As the design and construction teams grope around searching for the cause, your more flexible (than they originally wanted) truss would be the star of the show.

RE: Structural steel Transfer Trusses : Deflection limit

There are some instances where high deflection requirements make sense, others less so. No idea what this space is or what will be in it, so I don't know if L/1000 is just a 'feel good' number for a layman or a legitimate technical specification.

I agree with 271828, though, that if the client is asking for a more stringent value than is the norm it's best to give it to them. If they can't give you a reason, then you might offer a second concept design of your L/600 and show them how much money it could save so they can decide if their value is really worth it. But if they say they want it, then give it to them if it's possible.

Sheave beams for traction elevators are limited to a deflection of L/1666.

RE: Structural steel Transfer Trusses : Deflection limit

Give them the difference in steel tonnage for L/600 vs L/1000.

L/1000 is OTT, but regardless, the “I told you so” factor is already in place now! As such, I’d tend to run with it.

RE: Structural steel Transfer Trusses : Deflection limit

If he wants L/1000, give it to him... it's his nickel. If you fail to do so, might bring on a lot of liability that you don't want... I've always wanted to do a truss with W21x201 chord sections... but, never had the need.

MIS... you don't even want to do that; it looks bad in court if you've influenced the client.

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

RE: Structural steel Transfer Trusses : Deflection limit

L/1000 is stringent but not that uncommon.

If a client wanted a heavier solution I’d happily give it to them.

RE: Structural steel Transfer Trusses : Deflection limit

The problem is with the differential settlement on the supported structure. At less than span/1000, the Australian concrete code requires that you check for the effects of differential settlement of supports.

A good designer should check for that differential settlement in all cases.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close