Edge Column PEMB

Edge Column PEMB

Edge Column PEMB

(OP)
Is there any way to do a 50' span pre-engineered metal building foundation having the main frame columns supported on the edge (next to 1.5" sheet ledge) of the slab if the footing does not extend past the slab? Wouldn't be able to count much of the footing area that extends underneath the building slab for allowable bearing pressure because of eccentricity? Or am I going crazy?

RE: Edge Column PEMB

I've done many small PEMBs supported on a stiffened slab edge; is that similar?

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

RE: Edge Column PEMB


The simplest reasonable foundation for this case, DOWN TURNED SLAB.

The figure ( copy and paste ) from Metal Building Systems ( by Alexander NEWMAN )

RE: Edge Column PEMB

(OP)
So there’s never a good place to add HVAC equipment to a PEMB if there wasn’t cooling to start with? Guess a packaged unit on the ground is the only answer?

RE: Edge Column PEMB

With PEMBs, there's never a good place to add almost anything, if it wasn't there to start with. On one project, they did a redesign for adding sprinklers.

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

RE: Edge Column PEMB

(OP)
How did they do that? Busted out concrete to put a new frame up to hold sprinklers? I'm guessing the CM/GC/builder was very understanding..

RE: Edge Column PEMB

They were added to the PEMB... they didn't think it was necessary to add them to the slab. It was just the added weight that prompted the re-design. I didn't do a re-design of the foundations for the added sprinklers.

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

RE: Edge Column PEMB

For clearspans 60' and less, or modular PEMBS that have interior columsn 60' or less, you can generally get a turned down slab to work as shown by HTURKAK. Turn-downs don't do well over 60' columns span. The work real good on 40' and less. Once you design for uplift, soil bearing is generally ok unless you have crane loads on the column.

The grade beam is like part of your foundation in the turn-down scenario. The foundation is more of a T-shape.

RE: Edge Column PEMB

I'm confused - are you asking about foundation design, or adding HVAC? Or are the two related in an as yet unstated way?

Ron247 is dead on with the foundation. Unless it's being used for crane operations or it has a 60psf+ snow load, uplift will control the size of the footings. It comes down to detailing the steel in the stiffer portions of the slab (turndowns, etc.) to resist it.

I've seen a few RTU additions to PEMBs - they cut a hole in the roof, put 4 pipe columns up from the slab with a platform, and patched the roof around it. PEMB didn't take the new loading. It's usually best to assume they have zero residual capacity.

RE: Edge Column PEMB

Quote (It's usually best to assume they have zero residual capacity.)


pipe

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close