Short circuit ampacity of ACSR wire

Short circuit ampacity of ACSR wire

Short circuit ampacity of ACSR wire

(OP)
I am trying to find a reference in a textbook to the amount of current ACSR wire can carry before it is damaged. As an example, 3/0 ACSR can carry 325 amps and there is a damage curve for it but it does not consider what happens if someone loads it to 500 amps for an hour.


Thanks,

RE: Short circuit ampacity of ACSR wire

I have not seen such a reference.
Since the designer based the clearances based on wind, ice, and loading; most likely the ACSR will sag until it contacts the conductors below.

RE: Short circuit ampacity of ACSR wire

The behavior of the ACSR conductor is determined through sag-tension calculations. If an ACSR overhead conductor is loaded continuously above rated ampacity as suggested, the mechanical strength of the conductor is reduced.

This will lead to a loss of mechanical life, possible, not instantaneous failure. However, permanent conductor deformation may compromise the electrical clearance to the ground that will be in violation of the NESC in the US similar to other international codes.

There is ACSR manufacturer data and commercial software available such as PSL-CADD, SAG10 software, etc that can determine the conductor behavior exceeding the thermal rating. The nomogram below is another source for illustration.


RE: Short circuit ampacity of ACSR wire

We had an instance where 1/0 was loaded way over ampacity on a three phase structure on arms with MGN.
The B(center) phase dropped enough until it hit the neutral, opening the breaker.
Load it enough it will eventually fall from weakened steel.

RE: Short circuit ampacity of ACSR wire

See IEEE 738/2006 IEEE Standard for Calculating the Current-Temperature of
Bare Overhead Conductors.

RE: Short circuit ampacity of ACSR wire

According to Ampacity for Aluminum and ACSR Overhead Electrical Conductors/1986 Second Edition of Aluminum Association Table 4-AMPACITY FOR BARE ACSR CONDUCTORS 325 A ampacity it is for 4/0 conductor [no sun and wind]. The ambient temperature 40oC and conductor temperature Tc=75oC.
If we consider formula from IEEE 242/ 2001 CHAPTER 9.5.2.3 Intermediate and long-time zones :
IE/IN%=SQRT(((TE-To)/(TN-To)-(Io/IN)^2*exp(-θ/K))/(1-EXP(-θ/K)*(230+TN)/(230+TE))*100
where:
IE is emergency operating current rating=500A,
IN is normal current rating=325A,
IO is operating current prior to emergency=325A,
TE is conductor emergency operating temperature 119,
TN is conductor normal operating temperature[75oC],
TO is ambient temperature,
K is a constant, dependent on cable size and installation type (see Table 9-5),
and considering the ACSR conductor as a small cable in air K=0.5 hrs. and θ=1 hr then the conductor reached TE=119oC if the load current was 325 A for long time period before and suddenly jumps to 500 A for an hour.

RE: Short circuit ampacity of ACSR wire

It sounds like you might want to review how the conductor based on ambient temp and wind or get a system to monitor the dynamic loading of the line. These are sag detectors or things like optical temperature sensors.

RE: Short circuit ampacity of ACSR wire

As with a whole family of question of similar ilk over the years, if you have to ask you're too close to the boundary. It stated out with, if the inspector has to measure the clearance you don't have enough clearance, regardless of what gets measured. Nobody gets rewarded for closest to the edge, but lots of peopled get reamed for being just shy of the edge. Give yourself plenty of room, room that doesn't require detailed calcs.

I’ll see your silver lining and raise you two black clouds. - Protection Operations

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close