Is it standard industry practice to sign and seal incomplete drawings to avoid change requests?
A colleague claims that it is standard industry practice to sign and seal incomplete construction drawings (approximately 90% complete) and issue them for bid as a means to avoid future change requests. He even left the status on the drawings that indicates they are 90% complete and not for construction. I have never heard of this practice and it goes against my understanding that signing and sealing drawings indicates they are complete and ready for construction so I'm questioning his claim that it is an industry standard. Has anyone else heard of this practice?
RE: Is it standard industry practice to sign and seal incomplete drawings to avoid change requests?
Here are links to the Virginia Law. Your requirements may be different.
18VAC10-20-760. Use of seal.
18VAC10-20-740. Professional responsibility.
I'm okay with that.
Brad Waybright
The more you know, the more you know you don't know.
In no instance does the signing / sealing of documents limit the ability of other parties to initiate change orders on a given project.
Converting energy to motion for more than half a century
Obviously a private entity (owner, contractor) could require stamps. But that is just because they want, not required.
IMHO a 90% stamped planset is a contradiction since the remaining 10% of the design could include changes that are not conform to code. And who determines a design is 90%?
It varies by jurisdiction. Here we provide a stamped design set to JHA for plan review. That typically is the basis of the bid. but the bid can have changes. Bid documents are not necessarily stamped, but often are. Once the contract is awarded, the contractor obtains the actual permit and builds. At the end the supervising professional signs that the building is substantially the way it was designed (from a code perspective). If during construction there are significant changes (change in egress path), there needs to be approval by the local JHA. Wherever you are located, the process may vary.
I agree with others who have mentioned that the seal is not what makes it complete, it's a "NOT FOR CONSTRUCTION" stamp that signifies it's incomplete. If you seal it and don't say it's not for construction, you're effectively saying it meets all relevant aspects of the code and can be built as shown.
-for budget purposes
-clearly marked as "Not For Construction"
-designed correctly for the 90% complete, and noted where design is "to be confirmed" at the other 10%
If the drawing wasn't signed/sealed, I would take it merely as a coordination drawing which would be covered in the initial T&C of the project.
Obviously the rules of law would apply and may interpret the signing/sealing differently as the jurisdiction varies. There is also some obvious liability issues that are involved. But I do feel that it is a practical necessity in some cases (not ALL) to issue drawings as described.
EDIT: You can also put a disclaimer under your stamp that says "Issued for budget coordination. Not for construction" or similar.
EDIT2: I'm not saying this is best practice, but it is practice that has evolved. There are inherent issues with doing this on the regular. And there is also some schedule tradeoff with trying to attain 100% before permit submittal...usually the schedule wins.
"(a) The purpose of the engineer’s seal is to assure the user of the engineering product that the work has been performed or directly
supervised by the professional engineer named and to delineate the scope of the engineer’s work.
"(e) Preliminary documents released from a license holder's control shall identify the purpose of the document, the engineer(s) of record and
the engineer license number(s), and the release date by placing the following text or similar wording on the title sheet of bound engineering
reports, specifications, details, calculations or estimates, and each sheet of plans or drawings regardless of size or binding, instead of a seal:
'This document is released for the purpose of (Examples: interim review, mark-up, drafting) under the authority of (Example: Leslie H.
Doe, P.E. 0112) on (date). It is not to be used for (Examples: construction, bidding, permit) purposes.'"
Note that state board rules may require items to be sealed even if the customer doesn't require it.
How did you advertise the plans and, perhaps more importantly, to whom did you advertise the plans.
If a contractor chooses to build off a set that says anything other than "issue for construction" that is at their own risk regardless of whether a seal is present.
We also have to be mindful of the standard of care. In most states, the standard of care is basically a "C" average (i.e the design doesn't have to be perfect, but has to pass). A 90% plan set should meet the standard of care, and the final 10% should just be utilized for tweaking some minor details that don't affect the public's health et al.
Once again, it is all about advertising and what you call the plans. The seal is to signify that they have been prepared under your direct supervision, but they do not certify that they are "perfect".
I'm pretty sure you're correct... that's been my understanding for the last 50 years...
I believe in NC it is not required.
Seems an unscrupulous contractor with some whiteout could take care of that note pretty handily.
The title block should list the revision as "ISSUE FOR PERMITTING". You can also buy encryption keys that lock the PDF after it is sealed. Printed off with whiteout would be an easy fraud to detect.
If a contractor builds off a permit set, that is at their risk. That set is to get the job permitted, not for construction.
alchemon - that doesn't work around here anymore. AHJs have started cracking down and anything that says not for construction or for permit only is instantly rejected. They want to review the set that will be built - otherwise they're wasting their time.
I've not had this issue in VA or NC, but I appreciate that it is driven by the local AHJ. I typically tell the permit folks that the difference between the Issue for Permitting and Issue for Construction are me addressing their review comments.
It'll be interesting to see if this becomes more of an issue over time.
I figured if I manually have to add that in Bluebeam, I may accidentally issue a review set and forget to add that in the PDF editor. If it is marked as review set by default in Revit, there is less chance to forget to do that.
No one ever asked me to stamp an un-finished design and IMHO, JHA is the only entity that as an actual reason to get a sealed design. Once we have a contractor, we provide them with the set the JHA approved so they can obtain the permit. That JHA approved set can be a bit different from the bid documents since the bid may have had addenda to make changes unrelated to code requirements. The set we submit to JHA for review is the complete set at the time. It just happens that during the JHA review and bidding, some changes come up. It is a bit arbitrary and subjective what a 70%, 90%, 99% completed design is. But what I submit to JHA is at that time considered 100% complete. It is possible to submit to JHA less than 100% in an emergency and time crunch. But that isn't good practice and should be the exception.
In retrospect I probably painted our AHJs in a bad light there. They aren't that rigid, and they realize they may force changes or designs may change in construction. We had an issue a few years ago with a lot of design teams rushing 50% sets in so they could get 'reviewed' and try to short circuit the process when the drawings were finally done. So as long as the design is 'done' and what you show is safe and buildable, you're good. But if you send back a set later with a revision bubble around every sheet, they won't treat you very nicely. Inspectors have also cracked down on wanting to see field revisions at least acknowledged by the city reviewer.
I always find this statement funny for new builds. Since it really just comes down the Owner picking a day and saying hence forth the plant is open and I am losing money. Yes, there are nuances with the just in time supply chain everyone uses, opportunity cost, interest, etc. but it really is arbitrary.
How arbitrary it is depends on the plant and company. Losing profit bc you're not selling widgets is very different from being penalized by a customer for not delivering parts of their widget on time. The first upsets the bean counter, the second digs your grave.