Feeder cable sizing bs7671

Feeder cable sizing bs7671

Feeder cable sizing bs7671

(OP)
Hi,
With regards to a feeder cable feeding a small building (bs7671) I have reading conflicting information on whether to use the diversified load or the undiversified load.

Say building load is 150kw then after diversity (0.8)and load utilisation factor( 90%) this drops to 108kw. For the sizing of the feeder cable would the design current be calculated from 150kw or the after diversity rating of 108kw?

Thank you

RE: Feeder cable sizing bs7671

Dear Mr. STONE85
"...With regards to a feeder cable ...(bs7671). I have reading conflicting information on whether to use the diversified load or the undiversified load. Say building load is 150kw then after diversity (0.8)and load utilisation factor( 90%) this drops to 108kw. For the sizing of the feeder cable would the design current be calculated from 150kw or the after diversity rating of 108kw?.."
1. It may be based on 108kW load.
2. Otherwise, why are you calculating "diversity (0.8)and load utilisation factor( 90%)" for ?
Che Kuan Yau (Singapore)

RE: Feeder cable sizing bs7671

(OP)
Thanks for this. That’s exactly what I was thinking.

RE: Feeder cable sizing bs7671

(OP)
Hello,
I have a further query related to this topic if that’s ok. Say we have have three machines each rated at 100kw at full load. From the information I have there is diversity and load Ultilisation applied. This lowers the three machines and the third machine load figure is extremely small. I believe it would be best to size each of the cables/protection for the full load of 100kw even if I’m reality they won’t run at full load.

Is there something I’m missing or would you size each based on it’s diversified load?

Thank you

RE: Feeder cable sizing bs7671

Dear Mr. STONE85
"...I have a further query ..... Say we have have three machines each rated at 100kw at full load. From the information I have there is diversity and load Ultilisation applied. This lowers the three machines and the third machine load figure is extremely small. I believe it would be best to size each of the cables/protection for the full load of 100kw even if I’m reality they won’t run at full load... or would you size each based on it’s diversified load?..."
I think you are confused. There are two different issues.
1. the conductor size from building A to B may the sized to taking into consideration of " diversity and load Ultilisation" . This is making the assumption that NOT all THREE motors are going to run at (100kW each) FULL LOAD at the SAME TIME , for long hours.
1.1 It does NOT mean that it "lowers the three machines and the third machine load figure is extremely small".
2. In building B, the incoming breaker and busbar (if any) may be sized to, see above 1).
2.1 However, each of the three breakers, conductor size and the motor thermal over-load on the starter; feeding to each motor shall be rated for 100kW, i.e. NO " diversity and load Ultilisation". This is to ensure that all the three motors can be loaded to 100kW full-load any time. Attention: NOT all three at full-load for a long time.
Che Kuan Yau (Singapore)

RE: Feeder cable sizing bs7671

(OP)
Thanks for this. Just to be clear.


From my second post. If we have three 100kw machines then the supply to each one of these must be rated for 100kw. The feeder cable supplying the building housing the machines may take into consideration that these machines will not all be running at the same time at full load?

Thanks again.

RE: Feeder cable sizing bs7671

Dear Mr. STONE85
".... Just to be clear....
1) If we have three 100kw machines then the supply to each one of these must be rated for 100kw..."
. YES.
2) "...The feeder cable supplying the building housing the machines may take into consideration that these machines will not all be running at the same time at full load?...[add for long period of time] ". YES.
3) BTW (SI unit of Power) is [watt], not [Watt] . But its (symbol) is [W] not [w]. Therefore, 1000 W = 1 kW not 1kw. The machine is [100kW ] not 100kw.
Che Kuan Yau (Singapore)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close