reduce AC voltage to match relay nominal voltage

reduce AC voltage to match relay nominal voltage

reduce AC voltage to match relay nominal voltage

(OP)
Hello,

I am trying to solve an AC voltage misalignment between a transformer and a relay.

The transformer steps down from 230V AC to 16V AC (15VA) while the relay bobbin nominal voltage is 12V AC, 90mA and has a resistance of 80Ω.
Given that this relay will not be "activated" frequently for lengthy periods of time (perhaps 3 a week and few seconds each time), is there a simple solution even if it is not efficient and wasteful?
(I cannot change the transformer’s secondary voltage because it drives a device that was designed for 16V AC)

Thank you
Alon

RE: reduce AC voltage to match relay nominal voltage

Dear Mr. alonjr
"...The transformer steps down from 230V AC to 16V AC (15VA) while the relay bobbin nominal voltage is 12V AC, 90mA and has a resistance of 80Ω. Given that this relay will not be "activated" frequently...".
There are two possible alternatives:
a) use [another transformer] primary 16V and secondary 12V or a little higher to ensure that the voltage maintained at 12V when the relay pulls in.
b) use [resistor bridge] method using a 15W wire-wound resistor total resistance of 17.77 Ohm; with an adjustable tap at 13.32 Ohm. Use an ohm meter to determine the location of 13.32 Ohm. Connect 16V to the 17.77 Ohm and than check the voltage at the 13.32 Ohm tapping. It should be around 12V. Move the tapping to say slightly higher than 12V in order to ensure that the voltage drop is OK during relay pull in. Attention! the resistor is HOT! this is NOT an economical solution unless this circuit is activated for a very short duration and hardly used, as you had stated.
c) refrain from using a [series resistor] method to drop 4V . The [voltage drop would be very high] which would prevent the relay operation during pull in.
These are small toys but nevertheless it is part of electrical engineering.
Che Kuan Yau (Singapore)

RE: reduce AC voltage to match relay nominal voltage

Dear Mr. Alon,
I don't think anything needs to be done.
You said the relay is actuated infrequently that too, only for a few seconds each time. I don't think the excess voltage can do any harm to the Relay. You can verify the relay literature for its withstand capability.
Moreover, 16V at the transformer secondary is no-load voltage and when the relay draws pickup current (that is typically many times the holding current of 90mA mentioned), the voltage at the relay terminals is likely closer to 12V than 16V. You can verify in the field.

RE: reduce AC voltage to match relay nominal voltage

I would tend to agree with the above. It's close enough that a couple of seconds maximum should be fine.

Trying it as is would be far easier than sourcing a 17.77ohm resistor.

RE: reduce AC voltage to match relay nominal voltage

Check if the transformer has different taps. If not, just let it be, you are fine.

RE: reduce AC voltage to match relay nominal voltage

(OP)
... wow ... what an active forum!

I'll try the "don't do a thing approach" and hope that in my circumstances, it will be good enough.
Thanks so much for all of you who responded.
@che12345, thanks for introducing me to a few new elec. eng. concepts, I had fun researching them.

RE: reduce AC voltage to match relay nominal voltage

First check the current/voltage curve of the relay.
Increase the applied voltage while monitoring the current. The current will be mostly linear with the voltage until the onset of saturation. That is the limiting voltage. Running into saturation will guarantee a rapid failure of the relay coil.
I would leave a 5% or 10% safety margin on the applied voltage. Don't forget that on some days and times, the grid voltage may run high.
Alternatively:
calculate a series resistor. Short the series resistor with a set of normally closed contacts on the relay.
Forget the resistance on AC. Use 12 Volts/90 ma = 133 Ohms impedance. 4 Volts/90 ma = 44.4 Ohms series resistance.
That should give 16 Volts pull-in, 12 Volts hold-in. Check your voltage IRL and trim the resistor if needed to get 12 Volts hold-in.

--------------------
Ohm's law
Not just a good idea;
It's the LAW!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close