What percentage of glycol do you use when you have outdoor air-cooled chillers?

What percentage of glycol do you use when you have outdoor air-cooled chillers?

What percentage of glycol do you use when you have outdoor air-cooled chillers?

(OP)
These chillers will be serving a 200 apartment hotel. The piping system is 4-pipe so I think they'll want to run it year round just in case someone is hot in their room but I'm not exactly sure if that's common or not. This is in Utah so it can get down to the negative temperatures now and then. All time lows can be -20 F although very uncommon. However, going 50% glycol seems kind of like a waste. Any insight on this is appreciated.

RE: What percentage of glycol do you use when you have outdoor air-cooled chillers?

Look up climate data and freeze and slush points of the typical percentages.
If the chiller would be off during the coldest days (which one could assume apartments) you cna afford the glycol to go slushy. If you need it to run on all days, like in a server room, you can't get it go slushy.

RE: What percentage of glycol do you use when you have outdoor air-cooled chillers?

We've gotten by with 60/40 mixes for military systems specified for -40C; it's admittedly pretty slushy, but's unlikely that there will that much cooling demand at -20F. Note the glycol saps the heat transfer capacity of the fluid, so you want as little glycol as you can possibly get away with.

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm

RE: What percentage of glycol do you use when you have outdoor air-cooled chillers?

Running more glycol might seem wasteful but as you reduce the amount of glycol you increase the amount of water in your system and will now be spending more money on treatment.

RE: What percentage of glycol do you use when you have outdoor air-cooled chillers?

Running higher percentage of glycol than needed for burst or slush protection will unnecessarily reduce thermal properties and increase pump power. Especially for cold applications.
I've never seen a glycol system with chemical feeder. The fluid is for life (whose life?) Water systems have chemical feeders. You will want a glycol fillstation, though.

Also consider if you use PG or EG. For environmental reasons EG is on the way out (it seems).

RE: What percentage of glycol do you use when you have outdoor air-cooled chillers?

EG has ever so slightly better flow at cold, though, but yeah PG is much nicer, particularly with regard to any spillage. PG is also possibly less corrosive with steel, compared with EG.

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm

RE: What percentage of glycol do you use when you have outdoor air-cooled chillers?

(OP)
Thanks all, I decided to go with 40/60 propylene glycol solution. That should stop any freezing during the winter at my location.

RE: What percentage of glycol do you use when you have outdoor air-cooled chillers?

FacEngrPE: not sure where you are located. but here (US) the glycol you buy has everything included. Manufacturers have specific glycol for geothermal, chillers, solar, heating etc. they all have the (hopefully) appropriate additives to withstand the respective temperatures. For example, solar glycol is rated up to 350°F, while geothermal isn't. All the systems have a glycol fill-station and besides that are sealed. Glycol gets tested, and if pH, etc. are off, fluid gets replaced. Our systems are relatively small (fire station geothermal etc.). I assume for very large systems you could have some sort of manual maintenance of the fluid. but typically it is like a car, you replace if needed. You don't tamper with the fluid.
I wouldn't want the contractor just to start mixing stuff.....

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close