Wiring alternative for 3-phase heating circuit to reduce current
Wiring alternative for 3-phase heating circuit to reduce current
(OP)
Hi,
I have a tank that is used to melt glue. It has six heaters, each with a resistance of 10 ohms. It is powered with 208 VAC three phase.
Originally, it was wired as shown below with two heaters in parallel across each possible pair of lines (L1-L2, L2-L3, and L1-L3)...

I had asked a question yesterday about how to calculate the total current that this circuit would draw from L1, L2, and L3, which turned out to be about 72 amps. It turns out that this exceeds the rating of the breakers I have available to feed this circuit. With this being the case, I considered rewiring the heaters as shown below to reduce the current draw ...

... When I did the same current calculations (if I did them correctly), this decreased my expected current by a factor of four (down to 18 amps). This would make it easy for me to find a breaker to serve the circuit, but I am afraid that the corresponding factor of four decrease in heating power might make me unable to melt glue at my required rate.
I am wondering if anyone here can suggest another wiring alternative that would allow me to decrease the current draw by a factor that is less than four while still keeping my load balanced and having the same current flowing through every heater. I though about simply eliminating three heaters so that I would only hava a single heater across each possible pair of lines (L1-L2, L2-L3, and L1-L3), but I don't like this idea because it would mean I would then have less heated surface area in contact with the glue. I would really like to have current (albeit reduced) flowing through all six heaters. With six heaters and three lines, I just can't think of a way I can do this other than how I show in my second diagram (which results in a 4x reduction in power).
Any suggestions will be greatly appreciated.
Thanks and best regards,
Paul
I have a tank that is used to melt glue. It has six heaters, each with a resistance of 10 ohms. It is powered with 208 VAC three phase.
Originally, it was wired as shown below with two heaters in parallel across each possible pair of lines (L1-L2, L2-L3, and L1-L3)...

I had asked a question yesterday about how to calculate the total current that this circuit would draw from L1, L2, and L3, which turned out to be about 72 amps. It turns out that this exceeds the rating of the breakers I have available to feed this circuit. With this being the case, I considered rewiring the heaters as shown below to reduce the current draw ...

... When I did the same current calculations (if I did them correctly), this decreased my expected current by a factor of four (down to 18 amps). This would make it easy for me to find a breaker to serve the circuit, but I am afraid that the corresponding factor of four decrease in heating power might make me unable to melt glue at my required rate.
I am wondering if anyone here can suggest another wiring alternative that would allow me to decrease the current draw by a factor that is less than four while still keeping my load balanced and having the same current flowing through every heater. I though about simply eliminating three heaters so that I would only hava a single heater across each possible pair of lines (L1-L2, L2-L3, and L1-L3), but I don't like this idea because it would mean I would then have less heated surface area in contact with the glue. I would really like to have current (albeit reduced) flowing through all six heaters. With six heaters and three lines, I just can't think of a way I can do this other than how I show in my second diagram (which results in a 4x reduction in power).
Any suggestions will be greatly appreciated.
Thanks and best regards,
Paul
RE: Wiring alternative for 3-phase heating circuit to reduce current
Go to a wye connection. That will reduce your load by 67%.
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Wiring alternative for 3-phase heating circuit to reduce current
RE: Wiring alternative for 3-phase heating circuit to reduce current
"... It has six heaters, each with a resistance of 10 ohms. It is powered with 208 VAC three phase. Originally, it was wired as shown below with two heaters in parallel across each possible pair of lines (L1-L2, L2-L3, and L1-L3)..."
1. I am thinking by connecting [R1, R2 in series]; [R3, R4 in series], [R5, R6 in series]. Connect R1 to L1, R3 to L2, R3 to L3. Connect R2,4,6; in Y formation. This formation will result to [the lowest current] but check whether the heat produced (wattage) is sufficient to melt the glue.
2. Alternatively, R1, R2 in parallel, R3//R4, R5//R6. Connecting to the L1,2,3 ; in Y formation. This will produce more heat or higher (temperature).
3. Note: to achieve the heat you required:
a) it would required a certain current (amperage) with a fixed voltage supply source; no matter how you connect the heaters.
b) the [electricity bill] remains the same i.e. electrical power (wattage) input = heat output.
Che Kuan Yau (Singapore)
RE: Wiring alternative for 3-phase heating circuit to reduce current
Thank you for your suggestions. For the two options you mentioned (which I repeated below in italics), can you please let me know if the sketches I have inserted beneath each one accurately reflects what you have in mind? ...
1. I am thinking by connecting [R1, R2 in series]; [R3, R4 in series], [R5, R6 in series]. Connect R1 to L1, R3 to L2, R3 to L3. Connect R2,4,6; in Y formation. This formation will result to [the lowest current] but check whether the heat produced (wattage) is sufficient to melt the glue.
2. Alternatively, R1, R2 in parallel, R3//R4, R5//R6. Connecting to the L1,2,3 ; in Y formation. This will produce more heat or higher (temperature).
I appreciate your help with this.
Thanks again and best regards,
Paul
RE: Wiring alternative for 3-phase heating circuit to reduce current
If you connect three resistors in delta and three resistors in star, calculate the Watts of each group and then add. That is much easier than trying to figure the resulting sum of currents at different phase angles.
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Wiring alternative for 3-phase heating circuit to reduce current
Compared to the heaters in parallel and delta, the star connection will produce 28.9%% of the original Watts.
The total wattage of this connection will be 78.9% of the original wattage.
This is an interesting connection:
It will reduce the total wattage. How much reduction? I will leave the solution of that to my friend ElectricPete.
If I was to solve, I would start with a stated phantom current and work backwards to a voltage. I would then scale the voltage and current to match the 208 Volts.
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Wiring alternative for 3-phase heating circuit to reduce current
I'd probably "solve" that by wiring up six 100 W incandescent bulbs to a 208 V three phase supply and measuring and recording the voltages across all six resistors - and I'm intuiting that the bulbs would not blow.
Once the relationships and values of voltages are known, the current flowing in each resistor can be derived by scaling up, as the voltages relationships will not change.
Even thinking of trying to figure out how I would calculate the values mathematically / trigonometrically is making my head hurt . . .
CR
"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]
RE: Wiring alternative for 3-phase heating circuit to reduce current
xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.
RE: Wiring alternative for 3-phase heating circuit to reduce current
" ... For the two options you mentioned (which I repeated below in italics), can you please let me know if the sketches I have inserted beneath each one accurately reflects what you have in mind? ... "
" ...1. I am thinking by connecting [R1, R2 in series]; [R3, R4 in series], [R5, R6 in series]. Connect R1 to L1, R3 to L2, R3 to L3. Connect R2,4,6; in Y formation. This formation will result to [the lowest current] but check whether the heat produced (wattage) is sufficient to melt the glue...."
My apology, there is a typo error. It should be...Connect R1 to L1, R3 to L2, R5 to L3. I noticed you had got it right. It was my mistake that had caused the confusion. I am sorry for the inconvenience caused.
2. The second drawing, with resistors in parallel is in order.
Che Kuan Yau (Singapore)
RE: Wiring alternative for 3-phase heating circuit to reduce current
How is this solution:
5 Ohm resistor in the delta with 208 Volts three phase applied to the delta. 41.6 Amps.
Current to a corner of the delta = 72 Amps.
5 Ohm resistor at 72 Amps = 360 Volts.
Voltage from the delta corner to a calculated electrical neutral = 120 Volts. (This aligns the angle of the delta voltage with the angle of the wye voltage)
Total line to neutral voltage = 120 V = 360 V = 480 Volts
Edit: I forgot the root. 480V x 1.73 = 831.4 Volts, phase to phase.
480V / 208V = 2.308831.4V/208V = 3.997. or 4.
All currents and voltages may be scaled by 1/2.308 or multiplied by 0.433All currents and voltages may be scaled by 1/4 or multiplied by 0.25
Line current = 72 Amps / 4 = 18 Amps
Does that work for us, CR?
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Wiring alternative for 3-phase heating circuit to reduce current
Please see my previous post (including the linked file) for a much easier solution, Bill and CR. It confirms 18 A is correct.
xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.
RE: Wiring alternative for 3-phase heating circuit to reduce current
1. There are numerous ways of connection the 6 resistors (heater). They can be connected in series, parallel, in Y , D or YD formation etc.
2. I tried to work out four basic connections based on the resistor each rated 208V 10 Ohm on a 3ph 208V source.
2.1 in Y formation:
a) 2 resistors in series (10+10)=20 Ohm.
Line current = 6A . Total power of 6 resistors = 2161.5W
b) 2 resistors in parallel (10//10)=5 Ohm.
Line current = 24A . Total power of 6 resistors = 8647.2W
2.2 in [b]D/b] formation:
a) 2 resistors in series (10+10)=20 Ohm.
Line current = 18.01A . Total power of 6 resistors = 6488.21W
b) 2 resistors in parallel (10//10)=5 Ohm.
Line current = 72.05A . Total power of 6 resistors = 25958.4W
3. Observation:
a) No matter in Y, D or YD formation, resistors in series or in parallel connection; the (line current) is proportional to the [heat generated].
b) The (electricity bill) is proportional to the [heat generated].
Che Kuan Yau (Singapore)
RE: Wiring alternative for 3-phase heating circuit to reduce current
Unless and until the higher wattage triggers demand charges.
And less frequently
When paired with an inductive load a lower resistive load will be less buffering of the VARs of the inductive load and may trigger power factor penalties.
And that is not to mention non linear tariffs.
Actually, over the years, I have seen very few tariffs where the cost of electricity was directly proportional to the heat generated or the kilo-Watt-hours used.
The heat generated is proportional to the kilo-Watt-hours consumed.
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Wiring alternative for 3-phase heating circuit to reduce current
Thanks to che12345 for providing comparison calcs.
xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.
RE: Wiring alternative for 3-phase heating circuit to reduce current
Hi Bill, part of me wants to say, "Next time we plan to head BC/Alberta way, let's set something up."
The other part of me is thinking, "Eek! Face to face, Bill will find out how truly vast my ignorance is."
Hmmm, decisions, decisions . . .
Tell you what: next time my wife and I plan to head BC/Alberta way, let's you and I set something up.
CR
"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]
RE: Wiring alternative for 3-phase heating circuit to reduce current
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Wiring alternative for 3-phase heating circuit to reduce current
Less heat in a melting application means it will take more time to achieve the melt temperature, plus you run into the possibility of the heat losses in the melt vessel leaving you with never fully achieving it, i.e. your losses are faster than the heat gain at the lower wattage. So if you do reduce the heat to reduce the current, find a way to reduce thermal losses in your vessel.
Why do I say this? Been there, done that, got the T-shirt and the hat...
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
RE: Wiring alternative for 3-phase heating circuit to reduce current
A large liquid CO2 vessel. 2000 to 5000 gallons, and a set of heaters to vapourize the liquid.
During startup the process engineers couldn't get their pressure up. They hatched a plan to reconnect the heaters for more heat.
They asked me to reconnect the heaters for more heat. They felt that even at overvoltage, the heaters would not burn out as long as they were immersed in liquid CO2.
I did what they asked and reconnected for three or four times the heat.
They still could not get their pressure up.
They eventually discovered that someone had left a 1" purge valve open at the far end of the plant.
Once they closed the valve and quit venting to atmosphere, the pressure came up just fine.
I've seen the open valve syndrome more than once on startups.
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Wiring alternative for 3-phase heating circuit to reduce current
TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm
RE: Wiring alternative for 3-phase heating circuit to reduce current
Thank you all for your advice and calculations. I understand that reducing the line current will reduce my wattage and therefore my heating capability. When I undertook this project, I did not know how much wattage would be required to melt the glue in the tank at the required rate to keep up with the process the tank is supporting. I believe the original wiring of the glue melter was what Che described as Delta with two resistors in parallel (line current 72.05A; total power 25,958.4W). Knowing that this would be too much current for any available circuit in my building, I rewired the heaters to what Che described as Delta with two resistors in series (Line current 18.01A, total power 6488.21W)
I was concerned that decreasing power by a factor of four might reduce my heating capability too much for me to be able to melt glue at the required rate. That is what led me to post my question, hoping there might be an alternate wiring that would allow me to decrease my power and current somewhat, but by less than a factor of four.
As Che pointed out, rewiring in Y formation with two resistors in parallel would give me a line current of 24A and total power of 8647.2 W. This is about 33% more power than the 6488.21 W I am getting with my current wiring. I tried out the glue melter this week and my melt rate seems promising even with the 6488.21W. I am going to try it out to see if it can keep up with our process. If not, I may rewire for Y with two resistors in parallel to get the extra 33%. If this is not enough to keep up with the process, we will likely have to upgrade the supply circuit.
I really appreciate all of your help.
Best regards,
Paul
RE: Wiring alternative for 3-phase heating circuit to reduce current
Just a suggestion for your consideration
1. When you eventually settled on a certain wattage (say W1) that will melt and maintain the glue to the desired viscosity; it may? take (too long a time) to [heat up from cold/solid state]. A possible solution is to have a higher wattage (say W2), where W2>W1 to heat up at a shorter time. Switch back to W1 when the solid starts to turn to liquid.
2. Attention: Do not run on W2. It is intended for start up only. It may? over-heat the glue.
3. This change over from W2 (short time starting only) to W1 (long time running) may be by a [timer or a thermostat]. Or manually by observation the state of the glue.
Che Kuan Yau (Singapore)
RE: Wiring alternative for 3-phase heating circuit to reduce current
I didn't mention this in my previous posts, but power to the heaters is passed through an SCR that is controlled by a closed loop temperature controller. The temperature controller does timed proportioned control with (I believe) a one or two second cycle tim. With this control method, I believe that as long as I have enough wattage to achieve the required melt rate in the worst case scenario, the temperature controller should be able to reduce the average wattage (by decreasing the portion of each cycle when the SCR is ON)in situations when maximum power is not required.
I feel like I am just about ready to give it a try. I really appreciate your help.
Best regards,
Paul