High Temperature Soft Starter
High Temperature Soft Starter
(OP)
Can anyone make suggestions for soft starters that tolerate high heat and a bit of dirt? I need one for a 100 hp 3P 480V motor on an agricultural well in Arizona. Record high temp in the area where this would be installed is 124F.
I found a WEG that will tolerate 55C but I'd still like suggestions. I've been cruising your forum for a while and it seems like there are a lot of big brains on here.
I'm new to the forum so please excuse my ignorance of forum etiquette.
Thanks in advance.
Steven
I found a WEG that will tolerate 55C but I'd still like suggestions. I've been cruising your forum for a while and it seems like there are a lot of big brains on here.
I'm new to the forum so please excuse my ignorance of forum etiquette.
Thanks in advance.
Steven
RE: High Temperature Soft Starter
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
RE: High Temperature Soft Starter
This of course makes the installation, running and maintenance cost higher but if it is a crucial function it might be worth it.
Soft starters usually have a recommended limited amount of stopp starts in an hour, due to the heat development during start, something to look out for.
Maybe the old solution with Y/D start by contactors would be better.
Best Regards A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: High Temperature Soft Starter
RE: High Temperature Soft Starter
I know it's pathetic; but, it is what it is.
RedSnake - This is on a farm that's 2 hours drive from me. I'd REALLY like to avoid all the additionals that come with AC. Simple is good.
TugboatEng - They're autotransformer panels now. They've been baking in the Arizona heat for 30 years. Everything in the panel is rusty/crusty and buzzing and all the little plastic shit keeps breaking. The customer just wants them replaced so they'll be reliable.
It seems like the price of a single soft starter with internal bypass is comparable to two NEMA starters and associated control components/build time?
I probably should have started by letting you all know that I'm not an engineer. I'm a hack instrumentation and controls tech.
My company primarily drills/services wells. We have a small electrical division. They had one I&C guy that hired me and quit 4 months later. I've been figuring it out for 3 years. I never build panels but we are a 508A panel shop. I got my MTR cert a couple of months ago so I'm somewhat familiar with the process. I kinda want to handle this entire job myself. They're simple panels. Might be a good place to start.
That being said, I have a habit of biting off more than I can chew.
RE: High Temperature Soft Starter
https://search.abb.com/library/Download.aspx?Docum...
BR A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: High Temperature Soft Starter
If you want robust, the Allen-Bradley Bulletin 702 contactors were the best of the best but they have been discontinued. The Allen-Bradley Bulletin 500 and Square D Type S contactors are also very robust. Keep everything NEMA, use 30mm controls, derate all components, and avoid anything that says IEC when you build your new super panel.
RE: High Temperature Soft Starter
They can work for 10 to 15 years longer without a problem.
We exchange them as soon as they start bussing mostly because it's dam annoying.
But at 30 years at that environment they have done there time.
If you want a reliable and simple solution you should do as tug suggests and replace it with a new equal one.
Best Regards A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: High Temperature Soft Starter
Keith Cress
kcress - http://www.flaminsystems.com
RE: High Temperature Soft Starter
I decided to go with the SMC-50 and a sun shade. The enclosures are already ventilated. He feels pretty confident heat won't be an issue.
He confirmed what I kinda already knew. The autotransformer panels are pretty much obsolete now and when all is said and done they cost roughly twice as much as a solid state SS.
I appreciate all the input.
Should I post pictures when I'm done?
RE: High Temperature Soft Starter
/A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: High Temperature Soft Starter
Where in AZ? Just curious, I am west of Phoenix.
-AK2DM
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
"It's the questions that drive us"
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
RE: High Temperature Soft Starter
RE: High Temperature Soft Starter
Usually what drives the requirement for Reduced Voltage Starting (of any sort) is a starting requirement, often arbitrarily set by the utility at some value such as 50HP, 100HP etc. But Soft Starters on pumps also add a way to control the deceleration profile to avoid creating water hammer.
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
RE: High Temperature Soft Starter
I’ll see your silver lining and raise you two black clouds. - Protection Operations
RE: High Temperature Soft Starter
RE: High Temperature Soft Starter
What happens when tbe 500hp customer and the 200hp customer both start their motors simultaneously? The outside world loves to create worst case scenarios. Might as well require both to be on soft starters.
RE: High Temperature Soft Starter
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: High Temperature Soft Starter
RE: High Temperature Soft Starter
RE: High Temperature Soft Starter
I’ll see your silver lining and raise you two black clouds. - Protection Operations
RE: High Temperature Soft Starter
Keith Cress
kcress - http://www.flaminsystems.com