Contact US
Station Service Switchgear
Hey Guys,
For a service entrance rated switchgear, is the neutral bus and ground bus both bonded to the enclosure? I don't believe you would have a system bonding jumper like you would for a service disconnect in residential, for a switchgear where you have the ground bus spanning the length of the gear it would make sense to have the two busses bonded to the enclosure. The neutral bus would not be insulated.
We're talking 208V, 3 phase, 4 wire system.
EE
RE: Station Service Switchgear
If it is a 3-phase 4-WIRE system then the neutral has to be isolated from the ground and
should be sloidly grounded at the transformer star point ONLY before it enters the swgr.
If this is an installation in the US covered under the NEC: At the service entrance equipment, the incoming grounded conductor from the utility is connected to the neutral bus at the service equipment. There is a main bonding jumper that connects the neutral bus to the ground bus. The enclosure must be grounded. In addition, a grounding electrode must be provided. Downstream of the service equipment, the neutral must be isolated from the grounding conductor. Outside the US, I don't know.
Click Here to join Eng-Tips and talk with other members! Already a Member? Login
Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now
Close Box
Join Eng-Tips® Today!
Join Us             Close