Roof framing is 4 foot wide double tees, stems at 2'-0 with 1' cantilever flanges. stem thickness only 2" at bottom with slight taper upward. Building is in Atlanta GA built in 1967. Tee depth is 12" overall with 1 1/2" top flange no topping. Span is 40'. Any ideas on allowable loads?
RE: Old Double tee Roof 4 ft tees, 2" stems
From PCI 1st Edition (dated 1971) they have 4DT14 which is 14" deep but no 12" as you require:
Regardless, you will need to get info on the prestress content, so some semi-destructive field work will be required if you cannot locate the original drawings.
RE: Old Double tee Roof 4 ft tees, 2" stems
There is a brief historical discussion of the 4DT12: